Where the Dry type tranformers are used.
Answers were Sorted based on User's Feedback
Answer / ashish
Dry type transformers are used in indoor type substations,
mines etc. specially in hazardeous areas where oil cooling
may cause fire to take place.
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / minal verma
Dry type transformers can be located close to the load.
Locating the transformers close to the load may lead to
savings in cable cost & reduced electrical losses.
Drt type transformers can be use for indoor installation
like malls,Multiplexes.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / vivek
Dry type transformers are used where the oil cooled
transformers cannot be used considering safety point of
view for oil explosion. Mostly in indoor applications
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / raju
Dry type transformers can be located close to the load.
Is This Answer Correct ? | 0 Yes | 0 No |
A LT ckt i mean 440 volt flow of current100A.at this time HT current what will ON 11 KV &33 KV.plz givemy answer with example
What is the different between digital phase converter and ordinary phase converter?
Is it reuired to use house service barcket for 31/2 core 300 Sq.mm cable,if the distance between pole & shop is around 2 mtrs only or can I hang the cable with GI support in air? upto what size of cable GI serrvice btacket is necessary?
What loads the lagging and leading effects comes in a circuit?
What is defference between earthed and unearthed cable(HT)? Which is better for under ground cabling?
Generation of voltage for each phase are same of a turbogenerator.Although the short circuit current flow when two phase of turbogenerator are shorted(where current can't flow without potential difference),why?
Do you know how to joint the H.T and L.T Cables?
23 Answers KESC, MGVCL, Nokia, Oil Country Tubular, Power Control, SAGT, Siemens, Simco, Vivek Engineers,
why armature is placed in stator but not in rotor in synchronous generator ?
in ceiling fan and table fan what is the rotating part and what is the stationary part?
dg started in plc mode and load taken later one battery terminal connection will be disconnected by loose connection what will happen for dg and shall we connect battery terminals while dg in load time?
What is the pro & con of having 11kv & 33kv incoming, and what is the adv & disadv. of converting from 11kv to 33kv.
What Should be the value of Vector Surge angle at Tripping and how to calculate it?