I have 3KVA Libert GTX2 UPS. I need to calculate the back
up time with some load. How to calculate the Back time. I
need the expert guide
Answer / k.prakashchandra
The energy stored in each battery is = voltage of the
battery x AH of the battery in watt hour.If you multiply
this with the number of batteries ,you will arrive at total
energy stored in watt hour.This when divided by the load in
watts will give you back up time in hours.This method holds
good for both series and parallel connections of batteries .
Is This Answer Correct ? | 1 Yes | 0 No |
are there rmu for 3 transformer?
Why IR value of the (HT cable Plus synchronous motor) is less while individually having IR values in GΩ?
is it possible to step down voltage of single phase from a three phase sysem? explain
What happen when neutral point connected to core balance current transformer? (Neutral point of an alternator of a 180KVA DG. Neutral point connected to CBCT means enter to the CBCT)
0 Answers Great Eastern Energy Corporation Ltd,
why cannot we use a freuency more than 400hz is used in aircrafts?
I want to merge a cable..in between two metering Cubicals which contains CT's and PT's and Energy meter..before taking merger..what are the common things required?
Pls explain about vfd control?Where it is used, Give some example?
sent to a site and asked to explain how you would like a twenty seven flour building should be supplied with lighting and sockets plus a water boiler.
What is super thermal power plant? and how it will differ from normal thermal power plant
WHAT IS SITTING AMPS IN OVER-LOAD RELAY FOR 1PH OR 3PH MOTORS?IF ITS NAME PLATE GIVEN MAX AMPS 10AMPS?
3Cx240 & 3Cx300 sqmm Al. cable from lv side. What is the calculation for this cable??
we erected (48HP)63kva dist transformer and incoming from 11kv line,out going is 415v domastic line 2.04 km.for that actual output current is 84A. what are the losses and final output current.