I have 3KVA Libert GTX2 UPS. I need to calculate the back
up time with some load. How to calculate the Back time. I
need the expert guide



I have 3KVA Libert GTX2 UPS. I need to calculate the back up time with some load. How to calculate..

Answer / k.prakashchandra

The energy stored in each battery is = voltage of the
battery x AH of the battery in watt hour.If you multiply
this with the number of batteries ,you will arrive at total
energy stored in watt hour.This when divided by the load in
watts will give you back up time in hours.This method holds
good for both series and parallel connections of batteries .

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

are there rmu for 3 transformer?

0 Answers   OSC,


Why IR value of the (HT cable Plus synchronous motor) is less while individually having IR values in GΩ?

0 Answers  


is it possible to step down voltage of single phase from a three phase sysem? explain

2 Answers  


What happen when neutral point connected to core balance current transformer? (Neutral point of an alternator of a 180KVA DG. Neutral point connected to CBCT means enter to the CBCT)

0 Answers   Great Eastern Energy Corporation Ltd,


why cannot we use a freuency more than 400hz is used in aircrafts?

1 Answers  






I want to merge a cable..in between two metering Cubicals which contains CT's and PT's and Energy meter..before taking merger..what are the common things required?

0 Answers  


Pls explain about vfd control?Where it is used, Give some example?

3 Answers   Siemens,


sent to a site and asked to explain how you would like a twenty seven flour building should be supplied with lighting and sockets plus a water boiler.

0 Answers  


What is super thermal power plant? and how it will differ from normal thermal power plant

0 Answers   AK, Suzlon,


WHAT IS SITTING AMPS IN OVER-LOAD RELAY FOR 1PH OR 3PH MOTORS?IF ITS NAME PLATE GIVEN MAX AMPS 10AMPS?

0 Answers  


3Cx240 & 3Cx300 sqmm Al. cable from lv side. What is the calculation for this cable??

0 Answers  


we erected (48HP)63kva dist transformer and incoming from 11kv line,out going is 415v domastic line 2.04 km.for that actual output current is 84A. what are the losses and final output current.

3 Answers   Essar,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5084)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16631)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1094)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)