What is mean by CT Saturate? how do we calculate?
Answers were Sorted based on User's Feedback
Answer / s. puranik
Normally, CT is a Current Transformer. If the load current
is high, then this high current is allowed to pass through
its primary. Proportional load current is available at its
secondary. So a suitable meter can be connected to read the
secondary current which is proportional to the actual load
current. CT has its own capacity to give proportional
output current of its primary current. Upto certain
designed value CT gives proper proportional output of
primary current. But if primary current exeeds its primary
current designed value then CT does not respond to the
primary current proportionally but instead, the output
remains constant without any variations proportional to
primary or load current. This means CT is saturated.
| Is This Answer Correct ? | 13 Yes | 3 No |
Answer / rod
A CT saturates when a greater current is passed though it
than it was designed for, the way to test a CT (not design)
is to inject it with current until the curve flattens out,
the transistion curve is known as the knee point. It is not
calculated as such.
| Is This Answer Correct ? | 9 Yes | 2 No |
when we apply voltage between the secondary upto certain
limit it draws some mA exactly at the knee point the mA
will be double and if we cross the knee point then the CT
gets Saturated.
any of these effects are possible:
1.angle error
2.ratio error
3.secondary gets open
4.secondary simply acts as a conductor showing no ratio
| Is This Answer Correct ? | 1 Yes | 5 No |
Answer / guest
CT have some capacity to current carring at some voltage
level but some time we give more voltage to his capacity
that time ct passes more current up its capacity.
| Is This Answer Correct ? | 2 Yes | 10 No |
Answer / j.kesavan
ct saturate means when ct is open cicuite on load ct making
more sound and flashed.
| Is This Answer Correct ? | 0 Yes | 14 No |
can u tell the difference between star-star transformer and delta to delta transformer.
why after termination of HT cable armoured earth connected one end, why not connect other end.pls tell me correct answer.
What is gross error?
WHY IS THE NO LOAD CURRENT SMALL FOR A TRANSFORMER COMPARED TO OTHER ROTATING ELECTRICAL MACHINES??
sir i had plane to do some project with the base of hopkinson test in AC supply its possible
types of motors suitable for escalators with reason
what happen if transformer neutral not earth
Consider a case that two 200 hp motors are connected to 500KVA transformer. For improving power factor can we add capacitors in common bus bars to motors. Or should we add capacitors for each individual motor?
Why Transformer in KVA?
41 Answers APCPDCL, Apollo Power, College School Exams Tests, Electrical Tech, Hitech, HP, L&T, MDL, Oil and Gas Jobs, TATA,
IS THERE ANY ELECTRONIC CIRCUIT TO REDUCE THE NEUTRAL TO EARTH VOLTAGE BELOW 3V ?
why do harmonics generata?
Parts of machine and their discription in details with suitable photo
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)