in one substation we have two power transformers of
100mva,75mva capacity.statoin load is155mva.how much each
tranformers share the load????
Answers were Sorted based on User's Feedback
Answer / tara shankar gupta
Any system desined is to optimam utilisation,here we have
to Xmr ie 100 MVA and 75 MVA, connected load is 155 MVA in
this case we cant optimize 75 MVA Xmr. in such situations i
will suggest Maximam loading of Big Xme and Load rest MVA
to smaller one.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / asm
first you have to confirm that 155MVA is connected or
diversified load, if it is connected load then 90% loading
is coming. however if it is diversified load then u can
load upto 80% of transformer capacity. in this case X'mer
will be out of higher efficiency range.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / santhosh
both the transformer is same rating it would be share equal
load,i.e (trafo1=2000kva,trafo2=2000kva),current load is
2200kva, now trafo1=1100,trafo2=1100
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / k.prakashchandra
The voltage drops in the transformers + line should be equal
at the secondary bus-bar. Current shared by tr1 x its %
impedance = load shared by tr2 x its % impedance.Hence The
load sharing ratio is inverse to ratio of % impedances.
| Is This Answer Correct ? | 1 Yes | 0 No |
The load sharing will be in the inverse ratio of percentage
impedances. Lower the % impedance higher the load ,so that
the voltage drops are equal. .
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / harry
Higher Value Transformer u can Load upto 90% say 90MVA &
Lower Value Transformer u can load Load the Rest Say
remaining 10MVA.
It is General Practice to Do the Distribution of Load
According to above said manner
| Is This Answer Correct ? | 1 Yes | 8 No |
If a motor of 30KW rating &200 mtrs distance from feeder give me the cable size selection calculation?
how to reduce the transformer size in ups ?
why dc current is supplied in america rather than ac
why the neutral point in connnection oscillates?
function of apfc pannel
meter ratio is 100/5 CT ratio is 125/5, when the ratios changes i.e., CT ratio is 125/5 meter ratio is 100/5 what is the MF in boths conditions?
we have amp, voltage, kw, length detail then how to calculte copper & alluminium size of conductor of 3-phase induction motor
Sir if i have 2kv ups in which 17ah 8 battries load 600watts how much back up time i get and if i put 6kv ups with the same no of battries same amp can i get more back up time please give reply exactly what is the procedure to calculate back up time for different kv,s
why do we prefer -48 volt instead of -24volt or -12 volt etc. ??
What are the temperature elements?
What is the diameter of electromagnetic field around a 11000/415v transformer ? Dose it affect people who live 3-4 meter beside it?
What is the necessary condition for stability.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)