Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


in one substation we have two power transformers of
100mva,75mva capacity.statoin load is155mva.how much each
tranformers share the load????

Answers were Sorted based on User's Feedback



in one substation we have two power transformers of 100mva,75mva capacity.statoin load is155mva...

Answer / tara shankar gupta

Any system desined is to optimam utilisation,here we have
to Xmr ie 100 MVA and 75 MVA, connected load is 155 MVA in
this case we cant optimize 75 MVA Xmr. in such situations i
will suggest Maximam loading of Big Xme and Load rest MVA
to smaller one.

Is This Answer Correct ?    5 Yes 0 No

in one substation we have two power transformers of 100mva,75mva capacity.statoin load is155mva...

Answer / asm

first you have to confirm that 155MVA is connected or
diversified load, if it is connected load then 90% loading
is coming. however if it is diversified load then u can
load upto 80% of transformer capacity. in this case X'mer
will be out of higher efficiency range.

Is This Answer Correct ?    3 Yes 0 No

in one substation we have two power transformers of 100mva,75mva capacity.statoin load is155mva...

Answer / santhosh

both the transformer is same rating it would be share equal
load,i.e (trafo1=2000kva,trafo2=2000kva),current load is
2200kva, now trafo1=1100,trafo2=1100

Is This Answer Correct ?    4 Yes 1 No

in one substation we have two power transformers of 100mva,75mva capacity.statoin load is155mva...

Answer / k.prakashchandra

The voltage drops in the transformers + line should be equal
at the secondary bus-bar. Current shared by tr1 x its %
impedance = load shared by tr2 x its % impedance.Hence The
load sharing ratio is inverse to ratio of % impedances.

Is This Answer Correct ?    1 Yes 0 No

in one substation we have two power transformers of 100mva,75mva capacity.statoin load is155mva...

Answer / k.prakashchandra

The load sharing will be in the inverse ratio of percentage
impedances. Lower the % impedance higher the load ,so that
the voltage drops are equal. .

Is This Answer Correct ?    0 Yes 0 No

in one substation we have two power transformers of 100mva,75mva capacity.statoin load is155mva...

Answer / harry

Higher Value Transformer u can Load upto 90% say 90MVA &
Lower Value Transformer u can load Load the Rest Say
remaining 10MVA.
It is General Practice to Do the Distribution of Load
According to above said manner

Is This Answer Correct ?    1 Yes 8 No

Post New Answer

More Electrical Engineering Interview Questions

What is difference between safe PLC and normal PLC

0 Answers  


HAI,I HAVE 6,60KW MOTOR FEEDERS IN MY MCC PANEL.HOW CAN I DO MY SETTINGS FOR OVERLOAD,SHORTCIRCUIT,GROUNGFAULT,INSTANTANEOUS TRIP FUNCTION IN MY 4000A CIRCUIT BREAKER?

1 Answers  


what is the main function of contactor?????

9 Answers  


What is force on a conductor in a magnetic field ?

0 Answers  


How can we connect additional batteries to three phase ups? What are parameters we have to check when connecting?

0 Answers  


in three phase with neutral connection, what will happen,if the neutral is in open condition with single phase distribution panel ?

2 Answers  


Difference between UPS and Inverter?

7 Answers   HCL,


wht do u mean by load in circuit.wht dp u mean by inductive load

7 Answers   SGS,


How to calculate Battery back up time for a 400 AH Battery bank having a load of 20 Amps and charging time required to fully charge this battery bank?

2 Answers  


If we connect capacitor in series DC supply so what happened?

4 Answers  


what r the preventive maintenance of air compressor

1 Answers   Jindal,


Can we perform parallel operation of two transformers when one transformer on load?

3 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)