in one substation we have two power transformers of
100mva,75mva capacity.statoin load is155mva.how much each
tranformers share the load????
Answers were Sorted based on User's Feedback
Answer / tara shankar gupta
Any system desined is to optimam utilisation,here we have
to Xmr ie 100 MVA and 75 MVA, connected load is 155 MVA in
this case we cant optimize 75 MVA Xmr. in such situations i
will suggest Maximam loading of Big Xme and Load rest MVA
to smaller one.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / asm
first you have to confirm that 155MVA is connected or
diversified load, if it is connected load then 90% loading
is coming. however if it is diversified load then u can
load upto 80% of transformer capacity. in this case X'mer
will be out of higher efficiency range.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / santhosh
both the transformer is same rating it would be share equal
load,i.e (trafo1=2000kva,trafo2=2000kva),current load is
2200kva, now trafo1=1100,trafo2=1100
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / k.prakashchandra
The voltage drops in the transformers + line should be equal
at the secondary bus-bar. Current shared by tr1 x its %
impedance = load shared by tr2 x its % impedance.Hence The
load sharing ratio is inverse to ratio of % impedances.
Is This Answer Correct ? | 1 Yes | 0 No |
The load sharing will be in the inverse ratio of percentage
impedances. Lower the % impedance higher the load ,so that
the voltage drops are equal. .
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / harry
Higher Value Transformer u can Load upto 90% say 90MVA &
Lower Value Transformer u can load Load the Rest Say
remaining 10MVA.
It is General Practice to Do the Distribution of Load
According to above said manner
Is This Answer Correct ? | 1 Yes | 8 No |
What is the basic difference of turn ratio & transformation ratio for a transformer?
How can i learn to programme every VFD. Or is there any typical study to understand VFD programming.
can any one list the class-a, class-b & class-c trips of power generator?
why dc supply given to ac alternator rotor
what is a relay?
11kv alternator commissioning test?
WHAT IS BASICS TO SELECTION OF 11 kv Trasformer, send any calculation sheet for selection of transformer
what is the operating principle of contactor(power).along with disection?
3 Answers NASA, Tech Mahindra,
What is the difference between ARC & SPARK?
WHy neutral to ground trips when neutral touches the ground
How much load can take a 16 mm aluminum cable 3 phase
How we calculate the size of ht cable for any transformer