Why NGR is provided in sub station?..

Answer / jb

NGR means Neutral Grounding Resistance.it is used for limit the earth fault current.
generally the NGR earthing used upto the 11kv , Ac supply

Is This Answer Correct ?    3 Yes 1 No

Why NGR is provided in sub station?..

Answer / jithendra

NGR or Neutral Grounding Resistors are used to limit the ground fault current to a safe value in the event of earth fault. A NGR limits the earth fault current to a value which will be sufficient to operate protective relays and prevent unwanted fault damage.

Is This Answer Correct ?    1 Yes 1 No

Why NGR is provided in sub station?..

Answer / patni

Generator /Transformer neutral is grounded through resistor, called NGR (Neutral Grounding Resistor)which is used to limit the ground fault current to a safe value in the event of the earth fault. A NGR limits the earth fault current to a value which will be sufficient to operate protective relays and prevent equipment damage by excessive flow of fault current.

Is This Answer Correct ?    1 Yes 1 No

Why NGR is provided in sub station?..

Answer / arvind kumar

what is mean by harmonics 1
how can we minimize the off load losses of a distribution transformer which is required to be energized 24x7 ?? capacity of the T/F is 1250 KVA and off load losses are around 2.0 KW.. can we use capacitor bank at the secondary of such a T/F to overcome off load losses? please elaborate briefly...thanks 2
In alternator generally we give DC voltage to field of alternator but field (excitor)produce Ac & converts into DC by rotating rectifier(RR ) then fed to rotor .my question is why we cannot give dc voltage directly to rotor instead of Excitor & RR ? 1
How to calculate cable sizing 5
Why the bypass and blocking diodes are used in solar modules? 1
If a 1.5V,3W torch light bulb is connected in series with a 15HP/11.19KW,230V single phase motor and the combination is connected against a 230V supply and switched on than what will happen keeping all other parameters as it should be A)the bulb will glow normally B)the bulb will not glow C)the bulb will glow with extra brightness D)the bulb will burn out and if a fuse is connected to the above circuit will something happen to the fuse and what about the single phase motor will it be affected? Please explain with derivation 4
what is the best way to start a 15 KW motor for pump star-delta or direct on line ? and from how many KW i must use direct on line ? 1
what is HVDC, what are advantages over conventional system? 1
ohms law is applicable for dc or ac current or for both??? explain it berifly?? 2
what is unbalanced rotating magnetic field? 1
what size of copper busbar use for 11kv 630A 3
what is the maximum demand how it is defined 1

For more Electrical Engineering Interview Questions Click Here

Is This Answer Correct ?    0 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

During regenerative breaking= A rotating magnetic field is reversed B slip is positive C torque is positive D slip is negative

0 Answers   Core Solutions,


why ac wave is sinusoidal not square or triangular wave what will be reason

1 Answers   ACPL,


3 measuring instrument for transformers?

5 Answers  


Sir we have 12.5 MVA(110/11KV) transformer (Y-Y) connected,which tripped showing earth fault,when we charged transformer it stood OK ,but on connecting 11 KV feeders it tripped showing earth fault.our service engineers found that the B phase and R phase phase connecting to neutral broken from HV OLTC(on load tap changer),and R phase and Neutral is ok.Dissolved gas analysis shows that accetline content is high,tan delta value is 12.My dout is it is an internal fault of transformer,why REF or diffrential relay is not acted?

1 Answers  


what is effect of leading power facter on the system and billing

0 Answers   TATA,






What is the difference between isolators and electrical circuit breakers?

0 Answers  


what is ps impedance test

0 Answers  


What does VVVF stands for in VVVF drive ? How does it differ from VVF drive?

8 Answers   HAL,


why America use 60HZ 110V?

4 Answers   Kalindee Rail,


why the current is denoted by the letter 'i'

1 Answers  


what is the meaning of the HT LT transformer?

10 Answers   Sify,


Clearly Define Active,Reactive,Apparant power.Which applications used which power above metioned power?

9 Answers   Summit Power,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5084)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16631)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1094)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)