2 Diesel Generators 900KVA connected to the bus bar for
essential load as an alternative for power taken from
11/440V 3KVA Transformer supplying this bus bar. my
question here is in the event of power failure on 11KV side
can I feed the power to 11 KV bus by using the same
transformer as reverse feed, what will be the inrush
current???

Answers were Sorted based on User's Feedback



2 Diesel Generators 900KVA connected to the bus bar for essential load as an alternative for power..

Answer / joy

Your generator will be damaged. The reason being
that the transformer impedance as well as
impedeance of the entire 11kv side will be loaded
on the generator. Besides the inrush current which
the transformer will take when you charge it. This
will lead to the dropping of pf of the generator,
leading to the heating of its windings. Also you
have to make sure there are no chances of the
"normal" 11kv source being re applied when the
generator is being used to charge the 11kv side. Or
else the generator will experience a shearing of
its rotor.

Is This Answer Correct ?    7 Yes 1 No

2 Diesel Generators 900KVA connected to the bus bar for essential load as an alternative for power..

Answer / a. magesh kumar

My understanding is two 900 KVA generator, alternatively
feeds the supply to transformer (one at a time), the
transformer step down voltage 11KV/ 400V (3KVA). This 440V
feeds to connected load (seconday side of the transformer).

Ur question: In the event of Power failure 11KV side
(primary), what will be the inrush current?

whether u r asking short circuit current or else?



Inrush rush Current:



AC power may happen to be applied to the primary winding of
a power transformer at any point in the voltage cycle.
Excessive current inrush can result if the primary voltage
suddenly goes from zero to a high value rather than
increasing sinusoidally as it does during normal operation.
Excessive inrush current to a large transformer may not
only blow a fuse, trip a breaker, cause a sharp dip in
mains voltage, damage transformer windings, or damage
electrical supply circuits, it also induces a very large
voltage spike in the transformer secondary winding. Large
secondary voltage spikes can breakdown winding insulation,
damage rectifiers, and damage other power supply components
When switching power supplies are first turned on, they
present high initial currents as a result of filter
capacitor impedance. These large filter capacitors act like
a short circuit, producing an immediate inrush surge
current with a fast rise time. The peak inrush current is
several orders of magnitude greater than the circuit's
steady state current. This power surge can seriously damage
other components


Calculate the Steady State Current:
(Available data from ur mail)

Transformer power: 3 KVA

Primary Voltage : 11 KV

Secondary Voltage : 415 V

Efficiency : 85 % (assumed)

Impedance : 4 % (assumed)



Steady State Current: (KVA of transformer) / (efficiency
of transformer) X (Minimum Input voltage)

: 3 KVA / (0.70) X (415)

: 10.32 Amps.

Short Circuit Calculation: 3 KVA / 415
: 7.2 A
: 7.2 * 25 (impedance)

: 180.7 A (0.18 KA)



Short circuit current is 187.5 Amps.

Is This Answer Correct ?    5 Yes 1 No

2 Diesel Generators 900KVA connected to the bus bar for essential load as an alternative for power..

Answer / harsh

first answer is correct.
the generator will never damage while giving reverse
feedback.
its only to chack whether is there any fault in our cables
or any other machinery or furnaces.

Is This Answer Correct ?    3 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

what is the value of current as well as voltage upto which we will not feel shock and why?

3 Answers  


what are the effects when the frequency is decreased in any ac machine

1 Answers  


what is interpose? where it is used and why it is used?

0 Answers  


what is the purpose of vector group in a transformer ? if 2 tranaformers r connected in parallel the vector group is same or not? for parallel operation 2 transformers of different manufacturers maintain same vector group or not?

3 Answers   Orchid,


what is the difference between the alternator used in hydro and thermal power plants??

2 Answers  






How one can check the MAIN of a house wiring ?

0 Answers  


Which type of a.c motor is used in the fan (ceiling fan, exhaust fan, pedestal fan, bracket fan etc) which are find in the houses ?

0 Answers  


what will happen if u run induction motor beyond its rated speed

13 Answers   Adani, BARC, Bescom,


how many current required for hypo test

0 Answers  


What is the polarization index value ? (Pi value)and simple definition of polarization index ?

0 Answers  


What is the difference between AVR and Servo Stabliser

3 Answers   Wipro,


What is spike & surge.

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)