what is the difference between potential Transformers and
capacitive voltage transfoemers and where it is used?
Answers were Sorted based on User's Feedback
The purpose of VT and CVT in EHV system is same ie. to step
down the EHV to low voltage for measurement and protection
purpose. The extra function which CVT performs is to trap
the high voltage signals from the line which are used for
PLCC communication.
Is This Answer Correct ? | 19 Yes | 1 No |
Potential Transformer is designed for monitoring single-
phase and three-phase power line voltages in power metering
applications.
The primary terminals can be connected either in line-to-
line or in line-to-neutral configuration. Fused transformer
models are designated by a suffix of "F" for one fuse
or "FF" for two fuses.
A capacitor voltage transformer (CVT), or capacitance
coupled voltage transformer (CCVT) is a transformer used in
power systems to step down extra high voltage signals and
provide a low voltage signal, for measurement or to operate
a protective relay.
Is This Answer Correct ? | 15 Yes | 9 No |
the purpose of VT & CVT are same. but CVT use for High
Voltage line because we know high voltage surging can
disturbe your metering & protection accuracy so that reason
we use CCVT or CVT it has many capacitor to damp & stablize
all voltage during Surging and give smooth voltage.
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / ajay vikrant
The purpose of VT and CVT in EHV system is same ie. to step
down the EHV to low voltage for measurement and protection
purpose. The extra function which CVT performs is to trap
the high voltage signals from the line which are used for
PLCC communication.
Capacitance also reduces breaker TRV and steepness
overvoltage on the system.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / r.suryaprabha
Potential transformer is used for monitoring the voltage
CVT is a transformer used for measure the high voltage And operate the relay
Is This Answer Correct ? | 4 Yes | 13 No |
Hot Water System (HWS). Will a 30ma elcb have more nuisance tripping than 100ma elcb
The undesirable property of an electrical insulating material is
why in three phase 440 circuit in all phase current is almost equal L1-35 A,L2-34 A ,L3-31 A but in nutral when i check with clamp meter it shows 25 A?
How to size fuse? How to size MCB?
Can i connect all earth pits in ring system..., And wat IS 3043 says...please help me
why master trip(86) used in eletromagnet?
how do i convert 22kw to kva
How can we find the breaking capacity of a Load breaker switch (LBS) fed from 11 kv supply??ex:50KA, 26kA etc???detailed step vice answer pls.
The power consumption, in case of centrifugal loads (like pump, fan, blower etc.), proportional to ____.
how encoder works?
help!!!! i bought a new house 2 yrs ago,ive just had 2 new lights fitted,when i boil the kettle,maybe 2 times in succession the safety light switch trips out,it dosnt do it straight away but it seems to do it when the kettle boils!!!!! sounds very odd to me
why+ve is earthed in electrostatic precipitator in thermal power plant