Answer / narendra katakkar
First of all, a desired maintenance schedule is chalked out depending upon the diversity and intricacy of the installation. A typical maintenance schedule can be as follows.
1 Fix up a day (Maybe once a three months) and preferably when the installation is idle.
2 On that desired day the main power can be switched off, then disconnect all the neutral and body earth terminal connections.
3 Using Earth test instrument resistance of each earth station should be tabulated.
4 The earth stations to be properly watered or one can use drip irrigation system for continuous moisture retainment. If necessary add salt and charcoal or compound depending upon soil conditions. Excess of these materials to be avoided as this would lead to corrosion of earth electrode.
5 Check all the intermediate connections and remove rusted/corroded components.
6 Once again check the resistance values all the values should be below 2 ohms.
7 Connect back all the earth strips, on the power.
8 Fill up log book with noted resistance values.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / venugopal
Earth resistance is maintained 2 ohms.and now a days using chemicals also for earthing
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / pratik mistry
get earthing soil wet properly...and maintain it...checkout the needles and road
Is This Answer Correct ? | 0 Yes | 2 No |
why 3 phase is preferred than 1 phase?
what is charger supervision and control supervision?
why conductors of low tensile strength 1)produce greater sag and 2)can not be used for larger spans
Show the schematic arrangement of diesel power station layout and give its principle of operation.
What will happen 50 HZ motor when you will give 60 HZ?
7 Answers Bhushan Power Steel,
what is the purpose of ignitor in lighting fixer
How to select a cable size for particular load?
0 Answers Amit Enterprises, Takasago Engineering, Techno Electric and Engineering,
what must be the mf for a meter with the following conditions. line ct ratio-100/1 line pt ratio- 220kv/110v meter pt ratio- 3X63.5V meter CT ratio- -/1 A
Dear All, I am new in construction company , my boss ask a question at time of interview , If we have 60MW generation and Single Power Transformer step-up we have. if CMR 50/60MVA , ONAN, ONAF respectively , is it sufficient or not ? for that much power to transfer,
what is the voltage equation of 240/12 v transformer??
What is short circuit analysis of electrical networks?What are the procedures to be followed for its calculation?
why buchholz relay is kept on inclined position and why it is cover??