Actually why the transformers are rated in KVA.?
Answers were Sorted based on User's Feedback
Transformer gives apparent power,it is the supply power to load and the power actually used by the load is the
real power/true power/active power. Apparent power of 100 KVA has capacity to give 100 KW resistive load and for inductive load of o.8 pf it give 80 KW,and at 0.7 pf the same has capacity to give 70 KW . but the manufacturing company does not know which type of load to be connected across the transformer,therefore in simple we can say " DUE TO KNOWN POWER FACTOR THE TRANSFORMER ARE RATED IN KVA" and it is meaning less discuss about Iron loss & copper loss because the Inverted and UPS are rated in KVA but there is no iron loss & copper loss And in other hand in DC Generator there is Iron loss &copper loss but it is rated in KW not in KVA, because there is no angle between current and voltage(pf) in DC supply.
PRADYUMNA CHANDRA PANDA
Mob No- 9439721208
| Is This Answer Correct ? | 8 Yes | 0 No |
Edit- due to unknown power factor transformers are rated in kva
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kanchan kumar
This is becoz variable loss i.e copper loss is proportional to current and fixed loss i.e iron loss is proportional to voltage hence by combinig the both losses it will be product of current and voltage hence that is why rating is in VA ie due to high value it is in KVA
| Is This Answer Correct ? | 1 Yes | 1 No |
Transformer gives apparent power,it is the supply power to load and the power actually used by the load is the real power/true power/active power. Apparent power of 100 KVA has capacity to give 100 KW resistive load and for inductive load of o.8 pf it give 80 KW,and at 0.7 pf the same has capacity to give 70 KW . but the manufacturing company does not know which type of load to be connected across the transformer,therefore in simple we can say " DUE TO UNKNOWN POWER FACTOR THE TRANSFORMER ARE RATED IN KVA" and it is meaning less discuss about Iron loss & copper loss because the Inverted and UPS are rated in KVA but there is no iron loss & copper loss And in other hand in DC Generator there is Iron loss &copper loss but it is rated in KW not in KVA, because there is no angle between current and voltage(pf) in DC supply N:B . Transformer capacity -transformer iron loss & copper loss = transformer efficiency in KVA
PRADYUMNA PANDA BRG
Mob No. 9437917849
| Is This Answer Correct ? | 0 Yes | 0 No |
Is there any difference between circuit breakers and isolators
why are use corona ring in high tension line switchgear?
How to address the servo drive for motor
what is the difference between a frequecy converter and an electric inverter?
wat is the advantage of increse in frequency?how the powersupply range decreses as the frequency increses?like in america,it uses 110 ac and 60 hz?
What is A check, B check, C Check & D check for a diesel Generat
0 Answers Jtekt Koyo Bearings,
How many types of probe used in cro?
What is the control action?
How can we calculate ac current from the given DC current when AC voltage is given?
What is meant by Active and reactive power?
in telecom we are using neutral?
What is bushing?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)