Actually why the transformers are rated in KVA.?
Answers were Sorted based on User's Feedback
Transformer gives apparent power,it is the supply power to load and the power actually used by the load is the
real power/true power/active power. Apparent power of 100 KVA has capacity to give 100 KW resistive load and for inductive load of o.8 pf it give 80 KW,and at 0.7 pf the same has capacity to give 70 KW . but the manufacturing company does not know which type of load to be connected across the transformer,therefore in simple we can say " DUE TO KNOWN POWER FACTOR THE TRANSFORMER ARE RATED IN KVA" and it is meaning less discuss about Iron loss & copper loss because the Inverted and UPS are rated in KVA but there is no iron loss & copper loss And in other hand in DC Generator there is Iron loss &copper loss but it is rated in KW not in KVA, because there is no angle between current and voltage(pf) in DC supply.
PRADYUMNA CHANDRA PANDA
Mob No- 9439721208
Is This Answer Correct ? | 8 Yes | 0 No |
Edit- due to unknown power factor transformers are rated in kva
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kanchan kumar
This is becoz variable loss i.e copper loss is proportional to current and fixed loss i.e iron loss is proportional to voltage hence by combinig the both losses it will be product of current and voltage hence that is why rating is in VA ie due to high value it is in KVA
Is This Answer Correct ? | 1 Yes | 1 No |
Transformer gives apparent power,it is the supply power to load and the power actually used by the load is the real power/true power/active power. Apparent power of 100 KVA has capacity to give 100 KW resistive load and for inductive load of o.8 pf it give 80 KW,and at 0.7 pf the same has capacity to give 70 KW . but the manufacturing company does not know which type of load to be connected across the transformer,therefore in simple we can say " DUE TO UNKNOWN POWER FACTOR THE TRANSFORMER ARE RATED IN KVA" and it is meaning less discuss about Iron loss & copper loss because the Inverted and UPS are rated in KVA but there is no iron loss & copper loss And in other hand in DC Generator there is Iron loss &copper loss but it is rated in KW not in KVA, because there is no angle between current and voltage(pf) in DC supply N:B . Transformer capacity -transformer iron loss & copper loss = transformer efficiency in KVA
PRADYUMNA PANDA BRG
Mob No. 9437917849
Is This Answer Correct ? | 0 Yes | 0 No |
What are the two basic types of transformers?
how much watts are equal to one unit of energy meter?
What is reverse power relay?
what is the reason for earthing static equipments? why?
What is the basis for selecting Vk/2 or Vk/4 for REF and Differential protection of Transformer and What is the significance of magnetising current
what is difference between power & distrubution transformer ?
what is the principle of servo motor
how many transformer
what is power factor
WE HAVE A LOAD OF 55KW MOTOR ITS VOLTS 380 3PH AND ITS TAKING 100AMPS (ITS FULL LOAD IS 105AMPS)AND ITS CABLE IS 4CX50SQMM ,NOW ITS GETTING ABNORMAL HEATUP IN CABLE,PLZ TELL WHY ITS HEAT-UP?(CABLE LENGTH IS 15 METERS ONLY)
why fractional pitch winding generally used in alternators?
How to calculate the sag on transmission Lines.