I need to calculate the Battery bank back up for below configuration:-
UPS - 120 KVA
Battery Bank - 200Ah
Volt of each cell - 12 V
Total No of cell - 34 No's
Can you please help me to get the battery back up time for above configuration...? along with formula
Answer Posted / k.prakashchandra
Energy stored in each battery = 12 x 200 WH ( VAH) ,total stored energy = 12 x 200 x 34 WH . Divide this by load in W to get ' Back up time' in hours (approx)
| Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
When lag/lead/lag-lead compensation is employed?
how can we change the polarity of Alternating current rapidly? how frequency of ac can be controlled and changed easily?
In EHV transmission line a neutral grounding reactor is often placed at neutral point of shunt reactors. What is the recommended protection for this neutral grounding reactor? Should I use a fast closing switch to bypass neutral grounding reactor when this protection operates?
primery try cell?
how to know the diffrential relay setting of 06mva step- down (delta-star)transformer?
In diesel generator how AVR get voltage to excitation. And basic diagram DG EXCITATION CIRCUIT.
being an electrical engineer why you wanna come into software i have an very good academics what answer i have to give
if the load is 80 amp for main fuse and 100 amp for breaker so how can we calculate the cable size (cooper ) .
What is mason's gain formula?
What is minimum phase system?
how to generator maintenance (A Check, B check,Etc)
What is the current carrying capacity of 0SWG,3SWG,10 & 12 SWG solid bare overhead copper conductors?
what is the use of expulsition protective gap in 11Kv line.
In EB metering we face problem kva jump even in no load condition.can any one help to control this
How PADO software increase the efficiency of power plant?