Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Where should we terminate the shield and why?

Answers were Sorted based on User's Feedback



Where should we terminate the shield and why?..

Answer / carl_ellis

Shielding reduces electrostatic or capacitive coupled electrical noise in signal or communications cable

Electrostatic or capacitive coupling is proportional to the capacitance between the noise source and the signal wires. The magnitude of the interference depends on the rate of change of the noise voltage and the capacitance between the noise circuit and the signal circuit.

Electrostatic noise can be addressed by installing an electrostatic shield (also called a drain) around the signal wires. The currents generated by the noise voltages prefer to flow down the lower impedance path of the shield/drain rather than the signal wires.

The shield/drain must be of a low resistance material such as aluminum or copper. For a loosely braided copper shield (85% braid coverage), the screening factor is about 100 times or 20 dB. For a low resistance multi layered screen, this screening factor can be 35 dB or 3000 times.

The shield should be insulated to prevent inadvertent contact with multiple ground points, which could result in circulating currents.

The shield should never be left floating because that would tend to allow capacitive coupling, rendering the shield useless.

A single point connection to ground attempts to minimize the possibilty of ground-loop current that will flow between grounds at different potentials. A shield grounded at both ends can form a ground loop which can cause a processor to fault if those grounding points are at different potentials.

Vendors may specify grounding the shield at either the field end or the receiver end. When the shield/screen is grounded at one end only, the grounding is usually made in equipment panel/cabinet at the end with the power supply or the receiver. The field device end is left ungrounded and the shield/screen insulated.

At sites with equipotential grounding where the grounding is the same potential between grounding points, some vendors (Profibus DP's RS-485) recommend grounding the shield at both ends.

Cabling that runs through intermediate junction boxes shall have the integrity and continuity of shield connection maintained in the junction box without connecting the shield to a ground in the junction box.

The signal wire shield is never connected to the common side of a logic circuit (this would introduce noise into the logic circuit).

For high frequency RF noise rejection, a capacitor is inserted in series between the shield's drain wire and the ground connection.

For some communication network cables, the shield connections are unique to the particular cabling system. In some such cases, a dc short to ground is not needed because a low-impedance ac path to ground and a high-impedance dc path to ground are provided internally at each node. Follow the specific instructions in the publication provided for the specific communication network cabling system.

At any shield grounding connection, do not strip the shield back any further than necessary to make a connection.

Carl Ellis
Measure First

Is This Answer Correct ?    3 Yes 0 No

Where should we terminate the shield and why?..

Answer / praful lilhare

on Power supply side we should terminate but i dont know why?

Is This Answer Correct ?    1 Yes 0 No

Where should we terminate the shield and why?..

Answer / raja2016

Thanks to Carl_ellis...
you almost enlightened the purpose of shielding and its function....

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

1 bar is equal to how many pound per square inch(psi)?

14 Answers   Essar,


pl give the guidance for DUBAL written test

1 Answers  


i want interview questions about PROCESS CONTROL INSTRUMENTATION , SENSORS AND TRANSDUCERS IF ANY BADY KNOW ABOUT THAT PLEASE SEND TO MY MAIL karumudi1003@gmail.com

8 Answers   Honeywell, Reliance,


what is commisioning procedure,2)what is is the main work in commisioning in the field tx to dcs, plz send me detail

0 Answers  


what is puling in n pulling out in flame scanner system?

1 Answers  


what is the basic working principle of I/P and Positioner in any control valve.

12 Answers   Essar, Visa Steel,


(1) In turbine, what does term CDP, NI, NH, HSSOC, means. (2) What is the purpose of LO overhead tank in turbines.(3) An equipment is certified for EEX, IA, IIC,T6, what do you under stand by this.(4) what is SURGE, and how it is prevented, what is the purpose of bypass valve across AS valve.(5) Give 2 application of quartz crystal used for process parameter measurement.(6) what is meant by cold float of compressor shaft. (7) state four different types of flow measurement. For gas flow measurement mmscfd is the common unit. Expand the unit and specify significance of word S in the unit.(8) what is meant by Gap voltage, in vibration measurement. Normally how much Gap voltage is set and state the reason.(9) what will the new flow factor if D/P transmitter is Re-Ranged from 25” wc to 50” wc.(10) what is the usage of QDV & Volume booster.

0 Answers   ADMA OPCO,


I have 475 hart communicator. this is not support any new type of instruments such as tranmitter,fieldvue DVC6200.DVC 200 since i got point out need to upgrade . my questions is how can upgrade new instruments software in my 475 hart communicator. can any answerplease>?

1 Answers  


any body pl suggest me the best type of transmitter for level monitoring of a distillation still which consists of highly corrosive and inflammable liquid.closed vessel height=5000mm especially in petrochemical industries

1 Answers  


what is weighfeeder

2 Answers  


i want to Measure the Difference pressure of Packed distillation Column of height 3 mtr. h.p. side connected to bottom & L.P. side connected to the top , so tell me what will be THE URV & LRV of that D.P. transmitter?

5 Answers  


what is buoyancy law?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)