Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Where should we terminate the shield and why?

Answers were Sorted based on User's Feedback



Where should we terminate the shield and why?..

Answer / carl_ellis

Shielding reduces electrostatic or capacitive coupled electrical noise in signal or communications cable

Electrostatic or capacitive coupling is proportional to the capacitance between the noise source and the signal wires. The magnitude of the interference depends on the rate of change of the noise voltage and the capacitance between the noise circuit and the signal circuit.

Electrostatic noise can be addressed by installing an electrostatic shield (also called a drain) around the signal wires. The currents generated by the noise voltages prefer to flow down the lower impedance path of the shield/drain rather than the signal wires.

The shield/drain must be of a low resistance material such as aluminum or copper. For a loosely braided copper shield (85% braid coverage), the screening factor is about 100 times or 20 dB. For a low resistance multi layered screen, this screening factor can be 35 dB or 3000 times.

The shield should be insulated to prevent inadvertent contact with multiple ground points, which could result in circulating currents.

The shield should never be left floating because that would tend to allow capacitive coupling, rendering the shield useless.

A single point connection to ground attempts to minimize the possibilty of ground-loop current that will flow between grounds at different potentials. A shield grounded at both ends can form a ground loop which can cause a processor to fault if those grounding points are at different potentials.

Vendors may specify grounding the shield at either the field end or the receiver end. When the shield/screen is grounded at one end only, the grounding is usually made in equipment panel/cabinet at the end with the power supply or the receiver. The field device end is left ungrounded and the shield/screen insulated.

At sites with equipotential grounding where the grounding is the same potential between grounding points, some vendors (Profibus DP's RS-485) recommend grounding the shield at both ends.

Cabling that runs through intermediate junction boxes shall have the integrity and continuity of shield connection maintained in the junction box without connecting the shield to a ground in the junction box.

The signal wire shield is never connected to the common side of a logic circuit (this would introduce noise into the logic circuit).

For high frequency RF noise rejection, a capacitor is inserted in series between the shield's drain wire and the ground connection.

For some communication network cables, the shield connections are unique to the particular cabling system. In some such cases, a dc short to ground is not needed because a low-impedance ac path to ground and a high-impedance dc path to ground are provided internally at each node. Follow the specific instructions in the publication provided for the specific communication network cabling system.

At any shield grounding connection, do not strip the shield back any further than necessary to make a connection.

Carl Ellis
Measure First

Is This Answer Correct ?    3 Yes 0 No

Where should we terminate the shield and why?..

Answer / praful lilhare

on Power supply side we should terminate but i dont know why?

Is This Answer Correct ?    1 Yes 0 No

Where should we terminate the shield and why?..

Answer / raja2016

Thanks to Carl_ellis...
you almost enlightened the purpose of shielding and its function....

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

what are the installation requirement is common to all flow meter when volumetric flow rate is being measured

1 Answers  


difference between null and deflecting instrument.

5 Answers   ONGC,


Explain about relays.. Can we give both AC and DC to the same relay... How it is energising.. Explain its working..

7 Answers   IOCL,


how to draw a flowchart for swapping two numbers using bit wise operators?

1 Answers  


IF PLC POWER FAILURE THEN WHAT HAPPEN?

2 Answers   IFFCO,


Explain about safety integrated level protection? . How it was differ from other protections ?

0 Answers  


what is diff between sensors and transducers.explain with ex?

15 Answers  


whats the working of principal thermocouple

6 Answers  


How to zero trim the level transmitter by using foundation fieldbus communicator.

2 Answers   Emerson,


re i got gre score of 950,and toefl of 69 is this score sufficient actually my husband is presently in US i need to go please help me

1 Answers  


To find closed tank level by DP transmitter , how to findout its range.and insomeplace they using range like - 1500 to +1500 mmwc why not 0 to 3000 mmwc. how they spilit they range for minus and plus.and why?

1 Answers   Kuwait Oil Company,


how to calibrate a capillary type level transmitter for a closed tank in field? also what is the procedure for commissioning a capillary level transmitter for a closed tank?

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)