I want to know if flowrate increases in 16' pipe line what
will happen to upstream pressure and why?
Answer / carl_ellis
I want to know if flowrate increases in 16' pipe line what
will happen to upstream pressure and why?
There can be flow only if there is a differential pressure
to create the flow.
To increase flow rate, the differential pressure has to
increase.
To increase the differential pressure:
- the downstream pressure can decrease
- the upstream pressure can increase
- both upstream and downstream pressures can move in the
same direction, but vary in the magnitude of the change so
that the DP increases.
This principle applies to any flow, the size of the pipe
doesn't matter.
Carl Ellis
Measure First
Is This Answer Correct ? | 1 Yes | 0 No |
draw shematic diagram of c/v positioner(smart type)?
What are the key components of control loop?
WHY RESISTANCE TEMPERATURE DETECTOR IS AN ACTIVE DEVICE
HELLO FRENDS ,, I M IN THE MIDST OF TROUBLE .. JUST LITTLE HELP ME... SUPPOSE ,, I HAVE A CLOSE VESSELE TANK ( HEXANE MEDIA ) ,, I M USING ROSEMOUNT 2051 DPT FOR LEVEL APPLICATION .. ITS CALIBRATE RANGE IS.. . 0 TO 950 MMH20 ..I DID CALIBRATED DPT WITHOUT REMOVING IMPULSE LINE OF HIGH AND LOW TAPPING.. & WITHOUT DISTURB 3 WAY MANIFOLD..!!! BUT ,,, DURING CALIBRATION I SELECT RANGE BY HART LRV IS 900 MMH20 & URV IS 1300 MMH20 ,, BUT ,TANK LEVEL SOMETIMES 100 % AT 1100 MMH20 , SOMETIMES 1300 MMH20 ..IN THIS CONDITION .. WHOLE LOOP FAILED ,, MAIN THING IS THAT ,, HOW TO CUSTOME RANGE SELECT ?? AND IF I USED RANGE OVER THE ORIGINAL CALIBRATE RANGE ,,,THEN WHAT ERROR WILL BE COME ??? HOW TO ZERO CALIBRATION OF DPT... HOW TO ZERO TRIM BY MANIFOLD ?? AND FOR TANK LEVEL PURPOSE ... WHICH UNIT I CAN USE ??? IS THERE ANY CALCULATION OR CALIBRATION .. IF YEH .. THEN PLZ JUST GIVE ME CALIBRATION STEPS FOR DPT.. THANKS YOURSSSSSSS
difference between null and deflecting instrument.
what is pt100 RTD, and does 100 stands for
what the differant between Wet Leg /Dry Leg
Can any one tell me what type of question asked for instrumentation and control interview panel??? pls mail ramashankar.goel@gmail.com
What are the types of control valves available
Hi, Is there any smart plant instrumentation design training institute in Bangalore?
what is basic difference between motion balance and force balance in pneumatic instrument?
In dcs contol valve parameters showing like this Gain=1 or 2 , ti=7 sec, td=20sec. But temp,pressure,level control valves we are using in which type parameter side using ti,td clearly tell me