i have one tank of 500mm height, which is in under vacuum of
735 mmHg, I want measure level of the same using DPT , SO WHAT
WILL BE THE URV & LRV, DENSITY OF THE TANK FLUID IS 0.95. is
there necessary to fill the LP side with fluid.




Answers were Sorted based on User's Feedback



i have one tank of 500mm height, which is in under vacuum of 735 mmHg, I want measure level of the..

Answer / sam

First of all there is no difference between a vessel with a
process pressure of 10 or 50Bar or a vessel with a vacuum.
These pressures cancel each other across the LP and HP legs
on our tx's, and are therefore not taken into account in our
calibration.
To explain in more detail:
If there is 100Bar on the LP side there is also 100Bar on
the HP side so the DP across the tx is still zero.
If there is 750mmHg vacuum on the LP side there is also a
750mmHg vacuum on the HP side so the DP across the tx is
still zero.
So work with the transmitter as if there is no pressure or
vacuum in the vessel.

The best transmitter to use in a vacuum application like
this is a capillary type, but according to your question it
seems you already have a piped transmitter in place. This
makes it a bit more troublesome to do, but by working
carefully and accurately you can achieve accurate and
reliable results.

Take your time, this is one of the MOST DIFFICULT DP level
setup's you will ever came across in any industry.

It is always better to use a wet-leg since condensation will
cause your DP to chance in time. If I look at the sg of the
product you most probably are working with hydrocarbon
condensate, so you would want to install a wet leg in a
application like this.

Process zero with LP leg filled:
1st open both legs to atm and do zero trim. Even better if
you know how to do a factory reset and then do a zero trim.

Connect a 1/2" T-piece to top of LP leg just on the bend
before it goes to the top tap-off point with a needle valve
pointing upwards.
With main process isolation valves still close, fill LP leg
to max and close needle valve.
Try to use glycol since it's density is higher than water's,
and will prevent contamination of the wet leg.
You can also use glycerin or diesel.

Close 5-way manifold equalization valve and open main
process isolation valves and then only open both isolation
valves on manifold.
Open needle valve and fill again LP leg as much as possible,
start closing needle valve slowly and keep filling
to make sure lp leg is filled properly. Playing with the
main LP isolation valve and the needle valve will give best
results to get the LP leg filled to max.
This should put you in the situation that your tx has been
zeroed at atmospheric pressure, so the vacuum pulled
on both sides of diaphragm now and LP leg filled to max,
should now give a accurate process zero to work from.
Write down this displayed value.

What ever this value is is not important you will use this
reading as your process zero reference point to work from
so it can be anything as long as you are sure this is a
accurate and reliable process zero.
To double check if the process zero is good, isolate the tx
again and open it up to atm again not draining the LP leg.
It should still give a zero indication with both sides open
to atm.
Put it back on line and make sure the LP leg is still filled
to max by making use of the needle valve and LP main
isolation valve again.
You should be back at the previously displayed value. Do
this a couple of times to make sure you get to the same
values every time. Only then can you be sure that your
process zero value is reliable and accurate.

To calculate the LRV and URV:
Like I said I am assuming now that the tx had been installed
300mm below the bottom tap-off point.
I am also assuming that the bottom tap-off point is zero
position and the top tap-off point is 100%

You should now have something like (+/-) -750mmH2o on the tx
display.
Let's say the value is exactly -750mmH2o.

Measure from the middle of the tx's diaphragm to the bottom
tap-off point. We make this say 300mm
Measure from the bottom to the top tap-off points. We make
this say 500mm.

Calculation:
LRV is -750 + 300 = -450mm x .95 = -427,5 mmH2o
URV is -750 + 300 + 500 = +50mmH2o x .95 = +47,5 mmH2o

Modify your L/URV's to these new values. There is no need to
use a hand pump when working with smart tx's, just modify
the values with the HART, make sure it's on line and give it
back to production.

Since it is such a small span the level might be to
sensitive so you might want to increase the damping as well
on the Tx.
Good luck.

Is This Answer Correct ?    17 Yes 3 No

i have one tank of 500mm height, which is in under vacuum of 735 mmHg, I want measure level of the..

Answer / sam

Have to agree with Naman that this is not the best way to do
it and there are other devices that will work better if the
current instillation can be modified to accommodate a
different type of instrument like a capillary type of DP Tx
or a level troll.
According to question, the DPT is already in place and needs
to be used so above is the way to do it, and yes it is
possible to do since I have done it myself on a d-aerator
column under constant 0,98Bar vacuum and a span of only
300mm. My situation was the same in that I could not just
modify the installation and had to work with what was
installed.
Keep in mind that once the wet leg is filled the vacuum is
pulling against a closed end. Test this the next time you
drink a Coke out of a can . Suck the straw full and close
the end with your finger and try and suck the Coke
out.(please use a metal tube and not a plastic straw, LOL)
Good luck

Is This Answer Correct ?    9 Yes 0 No

i have one tank of 500mm height, which is in under vacuum of 735 mmHg, I want measure level of the..

Answer / muhammad irfan

thanks sam for incresing our knowledge
thanks once again..

Is This Answer Correct ?    2 Yes 0 No




i have one tank of 500mm height, which is in under vacuum of 735 mmHg, I want measure level of the..

Answer / sam

Thanks Nitin and you are more than welcome to give me a
shout is you get stuck again.

mass44@hotmail.co.uk

Is This Answer Correct ?    1 Yes 0 No

i have one tank of 500mm height, which is in under vacuum of 735 mmHg, I want measure level of the..

Answer / nitin

thanks Sam!
u really increased my knowledge.
& also i get the result

Is This Answer Correct ?    1 Yes 1 No

i have one tank of 500mm height, which is in under vacuum of 735 mmHg, I want measure level of the..

Answer / pavan

How can u get 300mm span ,send reply.

Is This Answer Correct ?    0 Yes 0 No

i have one tank of 500mm height, which is in under vacuum of 735 mmHg, I want measure level of the..

Answer / naman

i agree the above answe in case of wher vacum is not
present

if we r disussing about the vaccum ,,the vaccum will not
allow tha fluid to come in contact with tx. as same case
with in condenser
so we have to use here a float typ or displacer type tx. as
acc to me DP type will not work

Is This Answer Correct ?    2 Yes 9 No

Post New Answer



More Instrumentation Interview Questions

1,why we use 4-20 ma output of all instrument qhy not use 0- 20, 2,what is the different between PLC & DCS. 3,how can we meaure maximum span of new flowmeter if not given any information.

4 Answers   Reliance,


what are the use of belew gear in general ??

0 Answers  


1.what is the effect of vapour presuure in orifice plate flow measurement 2.which is more effective 2 pressure sensors or one single differential pressure sensor in orifice plate measurement 3.how to design a v/i converter and i/v converter 4.how many type of thermocouple are there 5.how many leads are there in thermocouple measurement 6.how pressure sensors are connected in level measurement in differential pressure method 7.what is the output of capacitive pressure sensor (ac or dc),how its o/p is signal charactarized 8.what is the physical meaning of discharge coeeficient,why it is calculated,orifice plate what is its value,why it is less than 1,Q at upstream is equal to or not equal to Q at downstream of orifice plate why?what is vena contracta in orifice plate 9.why rotameter is called variable area flowmeter,it can measure flow even if area is not varying,why it is made tapered 10.design a 10 bit counter ,which counter you will prefer 11.how to remove self heating error in RTD 12.which is more sensitive pt100 or pt50 13.why thermocouple are connected in parallel 14.what is lead contact error in RTD,how to avoid 15.what is P,PI,PID,PD controller,why there is no ID controller 16.what is override,split range,sequential,ratio,feedforward,cascade controller 17.why we moved from SR to JK and then JK to master slave JK flipflop,give correct reason 18.how to measure level of a closed container which contains vapour and liquid,remember no vapour gas should be leaked,so ultrasonic and capacitive is not an option,design another method 19.how to design horse race counter including sensors and signal conditioning element 20.what is bevelling

0 Answers   BARC,


wt is cold junction compensation

1 Answers  


For a diafhram 1.5 d =kn(p-p0) D4 Where d in deflection in inch k=constant n=no of capdule (P-P0)=Applied pressure in psi D In active dia at capsule. -1.5 d=k to p d being constant -1.5

0 Answers   L&T, Shiv Tech Marine Control,






can we create an interrupt in plc through scada?

0 Answers   TATA, Glensol,


Can any body help to get Rsemulator 5000 free from internet if possible then give me any link or any help .

0 Answers   Engro,


what is vibration a part of proceess variable? if vibration is a part variables then how we minimize the actual vibration on machine on load,? vision of instrumentation contrl plz ans me IPGDL interview question

0 Answers  


whats diffeence between dcs & scada operation.

3 Answers   Reliance, Orchid,


i have 80cm water tank.how can i use DPT as level mesurment.pls give specs for that..? We have air comp.from that moisture comeout to one tank.i want to mesure level of water in that tank and then after operat one sov to dicharge water after high level.

1 Answers  


how the flow rate is measured from a pipe with the help of pressure?

1 Answers  


why we use the ac supply load cell>?can we use the dc supply load cell?advantages and disadvantage of the ac supply load cell?

0 Answers  






Categories
  • Civil Engineering Interview Questions Civil Engineering (4638)
  • Mechanical Engineering Interview Questions Mechanical Engineering (3701)
  • Electrical Engineering Interview Questions Electrical Engineering (15777)
  • Electronics Communications Interview Questions Electronics Communications (2637)
  • Chemical Engineering Interview Questions Chemical Engineering (762)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (79)
  • Bio Engineering Interview Questions Bio Engineering (30)
  • Metallurgy Interview Questions Metallurgy (95)
  • Industrial Engineering Interview Questions Industrial Engineering (199)
  • Instrumentation Interview Questions Instrumentation (2879)
  • Automobile Engineering Interview Questions Automobile Engineering (171)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (41)
  • Marine Engineering Interview Questions Marine Engineering (62)
  • Power Plant Engineering Interview Questions Power Plant Engineering (170)
  • Engineering AllOther Interview Questions Engineering AllOther (1334)