Answer / ucmed_king
Refer Manufacturer coordination chart for required rating and model of MCCB.
There is a thumb-rule though. Convert KW to HP (KW/0.75), multiply it by 1.5 gives you the rated current. Multiply it by 1.5 for breaker value.
Here's the coordinartion chart:-
http://powertips-elec.blogspot.in/2010/11/selection-charts-for-dol-starters-l.html
| Is This Answer Correct ? | 9 Yes | 1 No |
Answer / akash
39Amp Per Phase is the actual load, but you can be on safer using side using 50/63Amp MCCB.
| Is This Answer Correct ? | 6 Yes | 0 No |
when the direction of a 3phase induction motor is reversed , is there any losses increases?
At which time Synchronous generator act as a Synchronous Condenser?
Why generally the Rating of Transformers are in additions of 11 i.e. 11 kVA, 22 kVa, 33 kVA, etc........
what type questions asked in hp cl
In what cases (circumstances)we should apply P controller, PD controller, PI controller & PID controller ?
what is meant by distance protection ? how distance protection relay function ?
how to select cable size according to ampere.
What is distance between electrical panel to land ?
What should be the setting of an earth fault relay.
how to find under ground cable fault ??? if our cable size is 95*4 then what will load capacity with far mull
what will be project cost for 100 kv transformer connection under oyt scheme.
What is AVR in Generators and How is it working.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)