Answer / ucmed_king
Refer Manufacturer coordination chart for required rating and model of MCCB.
There is a thumb-rule though. Convert KW to HP (KW/0.75), multiply it by 1.5 gives you the rated current. Multiply it by 1.5 for breaker value.
Here's the coordinartion chart:-
http://powertips-elec.blogspot.in/2010/11/selection-charts-for-dol-starters-l.html
| Is This Answer Correct ? | 9 Yes | 1 No |
Answer / akash
39Amp Per Phase is the actual load, but you can be on safer using side using 50/63Amp MCCB.
| Is This Answer Correct ? | 6 Yes | 0 No |
what is the main parts of transformer? how it is functioning? pls giv the ans briefly.
what is the relative size of single and three phase?
PLS SEND THE RRB CHENNAI MODEL QUESTION PAPER my email id is ganesan98655@rediffmail.com
we have one ups its neutral is not earthed.its one distribution MCB has a earth fault.but we can not put off any MCB.so how to find out that in which circuit is earthed without isolating the breaker.
What is EPBX????
if earthing is used in place of neutral how the circuit completd.
What are the advantages and disadvantages of negative feed back?
Diagram and details of polarity test for Current Transformer 11kv 400/200/100/1A
Brief difference btween aluminium & copper conductor
What is meant by time harmonics and space harmonics?
how to select a air/vacuum circuit breaker.is there any thumb rule???
what is the use of back emf?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)