For 415v,3phase,22kw rating of motor how to calculate MCCB rating
Answers were Sorted based on User's Feedback
Answer / ucmed_king
Refer Manufacturer coordination chart for required rating and model of MCCB.
There is a thumb-rule though. Convert KW to HP (KW/0.75), multiply it by 1.5 gives you the rated current. Multiply it by 1.5 for breaker value.
Here's the coordinartion chart:-
http://powertips-elec.blogspot.in/2010/11/selection-charts-for-dol-starters-l.html
Is This Answer Correct ? | 9 Yes | 1 No |
Answer / akash
39Amp Per Phase is the actual load, but you can be on safer using side using 50/63Amp MCCB.
Is This Answer Correct ? | 6 Yes | 0 No |
why does the magnetic balance tests at transformer?
HOW CAN I GET 5CORE HO7 CABLE SIZE IF I HAVE 1800A?
salam,hi, i need to know what the spesification of 300amp msb...
What is the formula to calculate capacitor bank rating for a certain load.
What are the disadvantages of LT AVR over HT AVR?
1 Answers APTransco, Jindal, TNEB Tamil Nadu Electricity Board,
WHY TERTIARY OF POWER TRANSFORMERS IS LOADED WITH EQUIPMENTS LIKE CT,PT,ISOLATOR AND CB
is there any device that works properly accept relay, it may be fuse but if i want fuse of 33kv 300 amp it is avaliable, pls give me details
what is settable hystersis protection? If any body knows plz kindly post the answer..
delta motor winding resistance I take normally single winding is 2.5, which value is came delta connection ie RY ?
why ct mensioned 0.5/5p20 plese any reply to me
in an electronic tri vector meter when the current and voltage sequence changes ? what is the effect of phase sequence on recording of meter
Can any one help me how to set an overload set the range from 2.8A to 4A , rated motor current 22A, CT 60/5A