What is AVR in Generators and How is it working.

Answers were Sorted based on User's Feedback



What is AVR in Generators and How is it working...

Answer / kumar,abb

hi iam AVR Service engineer .
AVr is heart og genset .its developing & maintain the
genset voltage as constant .its building voltage by
refernce of voltage produce by genset .for Ex: if genset
rated voltage is 11kv means intially genset produce some
minimum voltage (7- 14v)ac only is called resuidual
voltage .
that voltage is input of AVR .avr developing the
voltage upto rated Kv by some programmable circuit in
AVr .that O/p voltage is DC only its called as Excitation
voltage. we fed the excitation voltage to Excitor in
genset.after genset reached rated KV the AVr continusly
maintain the voltage as constant

Is This Answer Correct ?    17 Yes 0 No

What is AVR in Generators and How is it working...

Answer / satyanarayana raju

AVR MEANS AUTOMATIC VOLTAGE REGULATOR.AVR IS HAVING TWO
INPUT TERMINALS AND TWO OUT PUT TERMINALS OUT PUT IS GIVING
DC VOLTAGE .IT IS CLOSED LOOP CONTROL SYSTEM. I WILL
GIVE ONE EXAMPLE . AVR HAVING TERMINALS LIKE S1,S2, AND
F1,F2. S1 AND S2 ARE INPUT TERMINALS THAT IS CONNECTED TO
OUT PUT OF THE ALTERNATOR VOLTAGE. F1 AN F2 IS CONNEDCTED
TO FIELD OF THE EXITER TERMINALS. I WILL EXPLAIN HOW IT IS
WORKS. EXITER IS COUPLED WITH ALTERNATOR ROTOR. EXITER
FIELD IS HAVING OWN RESIDUAL MAGNITISUM DUE THIS MAGNETISUM
ALTERNATOR GETS SMALL VOLTAGE THAT IS AROUND 10-20VOLTS AT
OUT PUT VOLTAGE. U WANT SEE THIS VOLTAGE REMOVE F1 AND F2
CONNETIONS CHECK VOLTAGE AT OUT PUT TERMINALS. THESE OUT
VOLTAGE IS SENDING TO AVR INPUT TERMINALS THAT IS S1 & S2
THEN AVR GIVES SAME VOLTAGE TO EXITER FIELD THEN EXITER
FIELD GIVES MORE MAGNETISUM DUE TO THIS ALTERNATOR GIVES
MORE VOLTAGE AGAIN THIS VOLTAGE GIVEN TO AVR LIKE THIS
THESE CYCLES GOIES ON UP REACH REQUIRED VOLTAGE OF THE
ALTERNATOR. AT REACHING OUT PUT REQUIRED VOLTAGE AVR IS
NOT SENDING MORE VOLTAGE TO EXITER THERE IS CUTT OF SET
POINT . WHOLE THESE CYCLE TAKEN VERY LESS TIME MEANS MAY
BE 1 SEC. AVR OUTPUT VOLTAGE IS DEPENDS UPON THE COMPANY OF
THE AVR AND REQUIREMTNT OF THE ALTERNATOR. HELLOW FRIENDS
IF U HAVING LITTLE BIT KNOWLEDGE IN ALTERNATOR SIDE U
CHANCES A UNDER STAND THIS INFORMATION IS VERY EASILY. IF U
WANT MORE INFORMATION AGAIN CALL BACK . THNAKING U

Is This Answer Correct ?    8 Yes 1 No

What is AVR in Generators and How is it working...

Answer / lavanya

automatic voltage regulator

Is This Answer Correct ?    3 Yes 1 No

What is AVR in Generators and How is it working...

Answer / joel q.

AVR works as a regulator to the output voltage of the
generator. It's main function is to maintain a constant
amount of output voltage of for eg. 220V.

Is This Answer Correct ?    2 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

why transformer rating is given in kva?

2 Answers  


how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?

0 Answers  


What is the difference between MCCB & ACB Where it can be used

5 Answers  


what is the effect of power factor on DG supply,i mean to say what will the effect if we add capactors on dg supply.

4 Answers   HCL,


what is ferranti effect?

3 Answers  






WHATIS TIME CONSTANT? WHATIS ITS SIGNIFICANCE? ILLUSTRATE THROUGH EXAMLES.

0 Answers  


Define protection core in CTs Ex. 5P10, 5P20 etc.

1 Answers   HPL,


Why Dyn11 Transformer is selected for distribution transformer?

3 Answers   JK Associates, MSETCL Maharashtra State Electricity Transmission Co Ltd,


WHAT SHOULD BE THE BEST CURRENT RATINGS (PRIMARY / SECONDARY)FOR A CT INSTALLED AT THE INCOMING 11KV PANE? WILL IT BE CALCULATED ON THE BASES OF MAXIMUM DEMANT VALUE OR ON SUM OF ALL TRANSFORMER'S KVA? NOMALLY MAX DEMAND REPRESENT THE MAXIMUM OPERATING LOAD OF THE PLANT AND TOTAL KVA OF (SAY 5 NUMBERS TRANSFORMERS) REPRESENT THE CONNECTED LOAD. WHICH i.e. MAX DEMAND KVA OR CONNECTED KVA ARE BETTER TO USE FOR CT CURRENT CALCULATION? PLEASE ANSWER.

0 Answers  


What is the limitation of kirchoffs law?

0 Answers  


What is the function of Buchholz relay in transformer ?

1 Answers  


MCB MCCB ACB VCB

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)