1) What is difference b/w impedence relay and differential relay?
2) what are substations equipments?
3) what is difference b/w circuit breaker and isolator?
4)what are the types of circuit breakers?
5) which medium is mostlty used in circuit breakers and why it is used?
Answer / aariz ali
1)impedence relay is used for transmission lines protrction and diffrential relay is used for alternator protection.
also you can give their operational dirrerence.
2)ans: transformers, circuit breakers, isolators , realys etc ETC....
3)ans: the main difference is of the arc quenching medium which is only used in circuit breakers but not in isolator.
4) ans: air blast, vaccum, sf6, oil circuit breakers.
5)ans: SF6 medium is most commonly used because:
-sf6 gas is non inflammable so there is no any risk of fire in these ckt breakers.
-sf6 has high dielectric strenght so these breakers have short arcing time
- due to enclosed circuit these breakers have no moisture problem.
-small noise
etc etc.
| Is This Answer Correct ? | 3 Yes | 1 No |
We have studied about many techniques for finding the stability of system, ROOT LOCUS, ROUTH, BODE PLOT, POLER PLOT etc. In these which is used where. what are the difference among them... PLZ tell me.......
what will happen to give a dc supply in transformers?
how we select the mva rating of the circuit breakers?
why rating of generator is kva but motor is kw ?
with out name plate details , how to find the metering ct and protection ct.?pls brif explaination about that.
why are the likely reasons for bochholz & pressure relays oprate due to a internal fault but not differential relay ?
why inductivedrop in dc motor neglected
What is the effect of pd controller on system performance?
If a transformer primary winding operates at 240v, the secondary at 120v and the load is 1500w & the transformer is rated at 92% efficient, what's the current flowing through the primary winding of the transformer? What is the formula for finding this?
difference between high and low impedance BUS BAR relay??
diesel generator not getting start so whats problems will happen to DG and how we can start DG
Testing report of Earthing of 3.15 MVa PTR.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)