Answer / yusuf
Buchholz and Pressure relays such as Over Surge Relays are
also known as Gas operated relays... Consider an internal
fault such as inturturn fault in the transformer winding,
then the oil temperature raises which in turn produces Gas
inside the Oil Tank.. This Gas passes through the pipe
connected between Oil Tank and Conservator Tank and relay is
placed in the pipe work... so the Gas passes through the
relay and gives an alarm first and then trips the
transformer when the fault is severe.... Differential
protection is based on the principle of Differential current
which compares the current at the two sides ( LV & HV )of
the Trafo... And that's the reason the Differential
protection does not operate for incipient (Slow developing)
Faults
| Is This Answer Correct ? | 9 Yes | 0 No |
Answer / s.panneer selvam
I agree with the answer but i found that the differential relay is high impedance relay, in which we cannot used differential relay for transformer internal fault. Because due to mismatch in CT's and lead connection ur circuit will trip spuriously even if there is no abnormality when CT are requested for 100% protection. so we compelled to use some stabilizing resistor which creates non operative zone for some part of winding.where a incipient faults are not continous fault which exists in circuit , it is discontinuous fault after some it may not be in circuit.
| Is This Answer Correct ? | 0 Yes | 0 No |
Sir, plz tell me the relation b/w KW and frequency in Variable frequency Drive?
how many minutes or seconds taken by the transmission of electrical power from generating end to distributing end?
what is meant by impedence? can you describe easy becuse iam not well familier in electrical?
When we need up only in o/p 440v, so why we use directly in 11kva in input?
0 Answers Lupin, Medhaj Techno Concept,
single phase can run in PVC conduit. Three phase can also run in one PVC conduit. But two phase cannot run in one PVC conduit. WHY? reply plz....awaiting your answer.
explanation of mesh bus bars
How calculate cable size & voltage drop for the following requirement connected load 150 KW distance cable length 1000 M voltage 3 phase 415 v.
what are the affects of loose connection in electrical circuit.
EHV current carrying parts need to have smooth finish,then how can a 245kv GIS with emery finish can run so long?
in the thermal power plant, why we use the condenser (for cooling the steam) when we have to heat the steam again. i mean why we are cooling the steam,
wht d.c produces corrosion
is there a different b\w ground fault CB and earth leakage
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)