Answer / yusuf
Buchholz and Pressure relays such as Over Surge Relays are
also known as Gas operated relays... Consider an internal
fault such as inturturn fault in the transformer winding,
then the oil temperature raises which in turn produces Gas
inside the Oil Tank.. This Gas passes through the pipe
connected between Oil Tank and Conservator Tank and relay is
placed in the pipe work... so the Gas passes through the
relay and gives an alarm first and then trips the
transformer when the fault is severe.... Differential
protection is based on the principle of Differential current
which compares the current at the two sides ( LV & HV )of
the Trafo... And that's the reason the Differential
protection does not operate for incipient (Slow developing)
Faults
| Is This Answer Correct ? | 9 Yes | 0 No |
Answer / s.panneer selvam
I agree with the answer but i found that the differential relay is high impedance relay, in which we cannot used differential relay for transformer internal fault. Because due to mismatch in CT's and lead connection ur circuit will trip spuriously even if there is no abnormality when CT are requested for 100% protection. so we compelled to use some stabilizing resistor which creates non operative zone for some part of winding.where a incipient faults are not continous fault which exists in circuit , it is discontinuous fault after some it may not be in circuit.
| Is This Answer Correct ? | 0 Yes | 0 No |
IN MY INDUSTRIES 125 HP MOTOR USED FOR THAT ONLOAD AMPS UP TO 280 SO CAN I USE ONE LOWER KVA DG SET WITH STEP UP TRANSFORMERS THAT MEANS WITH LOW POWER INPUT TO GET CONSTANT HIGH POWER OUTPUT EG:125KVA DG SET = 250 KVA STEP UP TRANSFORMERS
Natural frequency in the control system represents nature of a. Transient response b. Oscillations c. Overshoot d. Speed of responce
How generating electric power export to grid from the generating station ?
how did the testing of protection relays done through current injection
what are the principles of a booster converter?
While elctrical load on DG,capacitor banks kept off why so? If capacitor banks on is their any effect DG?
4 Answers IL&FS Infrastructure Leasing Financial Services,
A rotor of an induction machine is delta connected. Now is there any necessacity to short the slip rings?
what are the breakdown voltage rating of mini- curcuit'transfarmer!
what should be distance between phase to phase in 415v system?
Which motor has high Starting Torque and Staring current DC motor, Induction motor or Synchronous motor?
what different in delta & star connection in motor?explain
5 Answers Bhushan Power Steel, Hyundai, KPCL, L&T,
what is the diffference between 3 point and 4 point starter ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)