with out name plate details , how to find the metering ct
and protection ct.?pls brif explaination about that.
Answers were Sorted based on User's Feedback
Answer / prasad asolkar
if we have both metering and protection ct at same place and if they are applicable for a single application then the thicker sized ct is protection ct and the thinner sized ct is metering ct.
for eg.
rated current of dg is 1000A
then, metering ct will be 1000/5A & protection ct will be 500/5A.
so for smaller rated ct requires more no of turns at primary therefore the 500/5A ct have thicker winding & 1000/5A ct will have thinner winding.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / gaurang harkhani
when name plate detail not given in CT the only thing that the first core is always metering ,second core is protection,Third core is differential.This is fore my knowledge of testing.
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / kmani190
i thing we we cna find from saturation testing but i dont
know correctly.pls clear it.
| Is This Answer Correct ? | 0 Yes | 3 No |
why dc supply is not applied for step up or down in transformer
Which of the following plant has less plant factor ? -Nuclear -Hydro -Diesel -Pumped storage
why substation rating interms of 11 multiples???like 11kv/33kv iis there any special reason???
what is the primary current in 415/415 v when secondry of dry type transformer is shorted.?
Different types of relay fault which phase sequence??
how to find out capacitor range?
What happens on the secondary of a 33kV/11kV when one phase of the primary fuse blows?
Which type of losses in transmission Line
what is the knee point voltage ? what is differtial rela? what is impedance and % of impedane? what is the postive phase sequance ? negative phase sequane ? and zero sequance impedance ? what is sortcircuit calculaion? why take calculation? define stabilty test ? why? what sentivity test? define merz protection ? what is the burden ? class 5p10, accracy, metering ct take knee point voltage test thet time what heppan why dont take knee point test to metering ct?
The maximum demand of consumer is 2 kW and his daily energy consumption is 20 units. Its Load Factor is (1) 10.15% (2) 41.6 % (3) 50 % (4) 60%
How to calulate cable size for 200KVA,160KVA& 40KVA load?
while selecting transformers for 33 kva feeder normally we ask for 33/433 kv why not 33/415
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)