with out name plate details , how to find the metering ct
and protection ct.?pls brif explaination about that.
Answers were Sorted based on User's Feedback
Answer / prasad asolkar
if we have both metering and protection ct at same place and if they are applicable for a single application then the thicker sized ct is protection ct and the thinner sized ct is metering ct.
for eg.
rated current of dg is 1000A
then, metering ct will be 1000/5A & protection ct will be 500/5A.
so for smaller rated ct requires more no of turns at primary therefore the 500/5A ct have thicker winding & 1000/5A ct will have thinner winding.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / gaurang harkhani
when name plate detail not given in CT the only thing that the first core is always metering ,second core is protection,Third core is differential.This is fore my knowledge of testing.
Is This Answer Correct ? | 1 Yes | 2 No |
Answer / kmani190
i thing we we cna find from saturation testing but i dont
know correctly.pls clear it.
Is This Answer Correct ? | 0 Yes | 3 No |
My ups output shows 230 v between phase and neutral,but show zero between phase and earth.Is the system/installation is correct.If not what will be the possible reasons
What will happen if 2 phase supply is given to 3 phase motor?
If we need4× 50mm sq cable but it's not available so we can pull 4×25mm sq 2cables
why fractional pitch winding generally used in alternators?
what is the relationship between phase & neutral
how can you size an automatic voltage regulator?
what are factors comes under relay setting (distance relay 7sa52) under OPEN DELTA VTs connection??
Two electrically operated Vibro Motors are fixed in parallel direction in vibrating feeder. What is the direction of both Vibro Motors?
as per standards how many neutral earthings and body earthings are needed.please help me
i am confused about generator. i have generator of 380 KVA that is 304 KW by that formula KW=KVA*0.8... then by this formula I=KW/V*1.732*0.8 the amperes are 528.673. so that is the load which i put on one phase of generator or this is total 3 phase load on Generator.......
can we connect PARALLEL 2 D.G set with different rating?? How ? What is the requirement for this connections?
Where is the center of magnetic field in alternator