if RTD damage in plant, how we know?
Answers were Sorted based on User's Feedback
Answer / anuj singh
First of all take a multimeter and set in resistance mode and measure if value is near 100 for pt/RTD at room temperature if value is nea zero then RTD is damage.
| Is This Answer Correct ? | 16 Yes | 0 No |
Answer / anuj singh
measure resistance by multimeter of RTD if it is near zero then your RTD damaged.
| Is This Answer Correct ? | 7 Yes | 2 No |
Answer / md gulfraj alam
sorry sir my english is touch week .. first take a multimeter and set in resistance mode and measure the rtd.if 100 ohm resistance at 0° centigrade then rtd pt-100 is ok near value 99-101 ohm resistance.and same case in pt50,pt25,pt500,pt100 etc only value is isolated of all rtd.otherwise rtd is damage when not match the value..i hope u understanding my ans.thank you
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / nvr
it can be known by two different way. first by measuring
resistance by using multimeter and second way to use
measure temp by using temp simulator.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / rahul singh
PT 100 means, 100 ohm at 0 degree. and 4 ohm increasing
with every 10 degree temp.
eg: if resistance show 120 ohm that means temp should be
show about 50 degree.
| Is This Answer Correct ? | 1 Yes | 1 No |
suggest a sensor to measure rapidly varying temperature?
how to given power supply of any type two wire transmitter in field?
why do 4 mA serves as 0% not 0 mA?
How to change dcs card in online. (Dsc is maxdna)
testing of thermo-couple?
What is the Difference between CNC and PLC
capillary type tranmitter using remote seals and capillary tubes filled with liquid of known of known density so if you wanna callibrate it just close block valve just before capilary @ high side & connect druck apply it's calibrated range pressure as normal calibration ensure low side block valve must be closed & if you asking commissioning so this is not a DP type pressure tx so simple if you wanna put in servie this tx just open high side block valve & than low side block same way i do it but still transmitter showing -13 ma.just tell me what i want to do ?
why Fahrenheit unit of moistur analyzer transmitter
why can't we use 5-20mA standard or some other instead of 4- 20mA?
HOW TO CALCULATE ACCURACY OF AN INSTRUMENT. WHICH IS COMPITABLE FOR USE.
in mass flow meter what is drive friquancy ?
how to change 4 wire rtd transmitter into a 3 wire rtd transmitter? as our transmitter is working for 4 wire rtd, what should do for working on 3 wire rtd transmitter
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)