In the field and in the control room different power
supplies if used How to handle the ground
Normally there should be different grounds in control room.
DCS or PLC vendor generally gives the drawing.
Mostly it is taken as convension that there should be 3
different grounding busbars in control room.
1. One is for the power earth. This will give the earthing
to the power distribution panel of the DCS or PLC.
2. Second is the Signal earth. All the shield cables will be
connected to this earthing busbar to minimize the
interference in the analog signal cables.
3. Thrd is Panel earth. This will be connected to the panel
body.
All these 3 busbars should be connected to 3 different
earthpits by 3 different Copper cables. Redundancy of
earthpits or copper cables may be there if possible.
| Is This Answer Correct ? | 3 Yes | 1 No |
why the output sugnal is 4-20 ma and not 4-25 ma?
How to calculate P,I&D value in PID controller ?
0 Answers Jindal Steel and Power, SAL Steel Power,
what is unit and element of viberation?
what are the programming languages used in dcs
how to calculate temp.prapotional to mv in thermocoulpe.
what is DCS and SCADA?
what is cascade controller ?
What is seismic transducer?Where it is used?
What is modbus?
please can anyone tell me in detail, what's mean by open loop and close loop?
How is PH sensor works ?
how to calibrate temprature switch and flow switch ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)