In the field and in the control room different power
supplies if used How to handle the ground
Normally there should be different grounds in control room.
DCS or PLC vendor generally gives the drawing.
Mostly it is taken as convension that there should be 3
different grounding busbars in control room.
1. One is for the power earth. This will give the earthing
to the power distribution panel of the DCS or PLC.
2. Second is the Signal earth. All the shield cables will be
connected to this earthing busbar to minimize the
interference in the analog signal cables.
3. Thrd is Panel earth. This will be connected to the panel
body.
All these 3 busbars should be connected to 3 different
earthpits by 3 different Copper cables. Redundancy of
earthpits or copper cables may be there if possible.
| Is This Answer Correct ? | 3 Yes | 1 No |
What is heating effect?
0 Answers Process Control Technologies,
how can calibrate pressure transmeeter in the feild ?
What is the Temperature Co-officient of Resistance of PT- 1000 and PT-2000 ?
What is pressure,What is temperature,What is flow,What is level
Why Boiler Drum level transmitter (TX) or level transmitter rang always put -600 to 0 other -900 to 0. Mines range why useā¦.?
why we use by pas on a positioner? When can a by pass be not used on a positioner ?
If mVolts can drop by resistance of wire as compare to mA, then how thermocouple mV reaches in CCR as accurate value?
Give 2 application of quartz crystal used for process parameter measurement.
What is the function of solenoid valve in on/off & shutdown valve and why it is not used in control valve normally?
A DP transmitter is used to measure the level of an open tank. The drain line of the tank is connected to a control valve, and is configured as, if the level of the tank is 90% the valve should get open 10%. And if the tank level is 10%, the valve should get open 90%. Draw wiring diagram and explain how to configure DP transmitter and control valve using HART communicator. If the span error at output is 1%, what will be the %opening of the control valve at 60% level of the tank?
Why Differential pressure transmitter is located below the tappings points for steam & condensible vapor flow measurement application?
Lux meter is the measuring device to measure the lux level of lighting fixture. in industrial sector two types of lighting fixture is being used as street lighting purpose 1. HPSV (Sodium) and 2. HPMV (Mercury). HPMV having white light which is an combination of red, blue and yellow colour, while HPSV haivng Yellow lighting. in HPSV red & blue colour will be absent. during measurement of the lux level of HPSV and HPMV fixture. 1. Lux meter can measure the actual lux level of both fixture? 2. or it will show false reading for HPSV fixture light as it has only yellow light present. please give me answer
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)