I want to use 1/2 inch SS316 tube in my high pressure &
temperature (64 kg/cm2 & 500 deg C)after condensate pot in
pressure tranmistter.
1) Is it possible to use 1/2" ss316 tube in high pressure
and temperature line.
Tube manufacturer is local vendor.
2)On sarting the plant, We need to do system fluse that
time condesate is not in the condesate pot so steam is
directly contact with the tube. We have no exact
calculation to know our tube is ok or nor at this time.
pleae,reply.
Answer / carl_ellis
1) Tubing comes
- in different wall thicknesses and the pressure rating
varies with wall thickness.
- in different material grades of stainless steel. The
pressure rating can vary with material
Your vendor should be able to supply the rating of the
tubing as determined according to a national standard like
ASME B31.1 and ASME B31.1 Process Piping from which
allowable working pressures are calculated from an S value
of XX,XXX psi (YYY.YY MPa) for ASTM A269 tubing at –20 to
100°F (–28 to 37°C), as listed in ASME B31.3 and ASME B31.1.
A factor (different factor for different temperatures) is
used to calculate the reduced maximum pressure at elevated
temperatures.
An example is provided in the Swagelok tubing catalog on
pages 2 and 3 for their tubing (not your tubing).
http://www.swagelok.com/downloads/webcatalogs/EN/MS-01-181.PDF
You need to run the calculation for your vendor's tubing.
2) You need to refill the tubing and condensate pots with
water after the flush but before steam is applied, otherwise
the steam will damage the transmitter.
Carl Ellis
Measure First
64Kg/cm2 = 910 psig
500 Deg C = 932 Deg F
Is This Answer Correct ? | 0 Yes | 0 No |
IF PLC POWER FAILURE THEN WHAT HAPPEN?
what's the criteria of using over range protector when installing Pressure Gauge
What are the reliability data ,like failure rate etc,for bently nevada systems & vibration probes.
Calibration of flow transmitter.
Introduce yourself which is not present in your biodata?
we have a s-5 simense plc having op7 .recently on op7 showing error 1.plc not present 2. DB error frequently. can u have any solution . please send me.
can we create an interrupt in plc through scada?
what is diffrence between cascade & three element system.
Explain PID controller tuning & any one method used for it.
What are the charcterstics of a P&ID controller block for Governor speed raise or lower for a load sharing functionality between 4 Gas turbines in droop mode.
How to convert ma to mv? Resistance 250 ohm is connected in series or Parallel?
How to find out the current of two motors having same power consumption but different RPM?