how long will take to burst/damage for a CT when secondary
in open condition?
Experienced: During switchgear testing(Primary current
injection test) some of the CT are in open condition, but
nothing happen's why?
Answer / sheikh
Every one C.T has it,s saturated voltage status which called
knee point voltage if any one ct has been crossed over the
limitation of knee point then will be chance to burnt out
the ct .
| Is This Answer Correct ? | 2 Yes | 1 No |
why the voltage transmission is always in a multiple of 11? e.g. 110 V, 220 V, 33 kVA, 11 kVA
In between UPS out going changer over switch and ups raising main input, both side cable gland producing heat but the cable doesn't get heat,Why?
Why we generate power at multiple of 11 i.e 11kv,33kv etc.
9 Answers DTV Solutions, Havells, TCS,
what is meant by motor protection relay & its working principle ?k
What is CRT (Contact Resistance Test) for Isolators or Dis- connector Switches? Why we performed it & whats the Testing procedure.
What is the permissible value of earth resistance!
if acapacitor connected to power supply will it cosume power& will it going to get recorded in energy meter
Why we are using LA Rating 10kA in 66 kv substation
Why 11KV/440V distribution supply use for Domestic use?
3 Answers Essar, Getco, Nissan,
how much current take 16sq mm Cable
why dimmerstate always connected in star connection? what will happen if it connected in delta?
-What is leakage current . how much leakage current is allowed.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)