how long will take to burst/damage for a CT when secondary
in open condition?
Experienced: During switchgear testing(Primary current
injection test) some of the CT are in open condition, but
nothing happen's why?
Answer / sheikh
Every one C.T has it,s saturated voltage status which called
knee point voltage if any one ct has been crossed over the
limitation of knee point then will be chance to burnt out
the ct .
Is This Answer Correct ? | 2 Yes | 1 No |
Why use only DC supply to charge batteries why not AC Supply??
What is the function of a capacitor in a ceiling fan?
In CT, burden is 15 VA and protection 5P20,CT ratio is 100:1 then what would be the knee point voltage ?
A single line diagram(SLD) and a purchase order of a 11/66kV switchyard of a power plant was given. In the SLD, only one lightning arrestor(LA) was shown, but the purchase order had need of 3 LAs. Is this correct, if yes, why?
why single phase induction motors are not self staring ? how can we start the 1-phase Induction motor ?
how to improve my communication skills
7 Answers Infosys, MAHINDRA, Wipro,
How to calculate phase to phase difference in 33KV Line ,11KV Line etc.
Why transformer use to generator neutral earthing purpose ?
During Testing of Maintenance Free Earthing, How deep should be the Spikes of Earth Test Meter should be inserted in the soil(one spike is 15 Meter & Other spike is 30 Mtrs away from the Main Earth Electrode. Because, recently, we observed that when spike is inserted 3-4 Inch in the earth- results are better, If spike is inserted 1 feet deep than results are increasing.
What happen if we have run 415 V,50Hz designed motor at on 480V,60HZ
Why does The speed of motor used in elevator remain constant irrespective of load??
What is meant by celling voltage & current in excitor ?