-What is leakage current . how much leakage current is
allowed.
Answers were Sorted based on User's Feedback
Answer / shao
Leakage current is the current that flows through the protective ground conductor to ground. In
the absence of a grounding connection, it is the current that could flow from any conductive part
or the surface of non-conductive parts to ground if a conductive path was available (such as a
human body). There are always extraneous currents flowing in the safety ground conductor.
If you are doing testing at HV equipment. in that case (0.1-0.9 Micro Amperes) leakage currents values are acceptable.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / v.sudhakar reddy
Leakage current is the current that flows from the unit
through the grounding conductor into a household ground.
Leakage current could shock an individual if the household
grounding is not sufficient or there is an intentional or
unintentional interruption of grounding connection maximum
leakage current 0.5MA
Is This Answer Correct ? | 8 Yes | 6 No |
Leakage current is wastage current which occurs due to
improper insulation within the unit, and is also dangerous
by direct human contact. Leakage may be between,
Input to ground,
Output to ground, or even
Input to output terminals.
According to IEC standards, 10mA flow is accepted when 2kV
is applied across the above mentioned terminals when they
are electrically isolated.
Is This Answer Correct ? | 2 Yes | 3 No |
wht d.c produces corrosion
1. A bomber drops a bomb from an aircraft flying at 2000 km/hr. at an altitude of 7km. The speed at which the bomb will strike the earth would be
Why (In India) we preferably go for +-30 deg connection of transformer? what are the advantages in this connection?
in general it is observed in power stations, the tertiary winding is used in higher rating Y-Y auto transformer but not in Y-Y power transformer. is the tertiary winding is compulsory then why it is not using in power transformer
What is different between hypo test and megger test
what is inverter and converter
7 Answers Shrishti Power Technologies,
what is the distance b/w EHV lines? 1.8m 2.11m 3.4m 4.14m
Supose we have one 220v A.C fan.if we provide 220v D.C what will be happen?
What are formula we can apply to determine the HT/LT current of 11KV/433V transformer except KVA/LV×√3. ?
why high current produce in case of transformer when turns are internally gets shorted.
how calculate gd2 of ht motors
0 Answers Hindustan Copper Limited,
Why is water motor not taking the pressure? what is the problem?