What is the permissible value of earth resistance!
Answers were Sorted based on User's Feedback
Answer / rkshjangra
For large power station = 0.5
for small substation = 2.0
for domestic wiring = 5.0
| Is This Answer Correct ? | 36 Yes | 4 No |
Answer / p.gupta.1852
Earth resistance should be as small as possible . It
depands on voltage level of the system to be grounded . As
voltage level increases the earth resistance required to be
nearer to zeero as far as possible . Earth resistance
should not exceed 5 ohm for 433V distribution system and
should be below 1 ohm for 66 KV Grid .
| Is This Answer Correct ? | 26 Yes | 4 No |
Answer / mahesh babu-calicut
the earthing resistance of any electrical system should be
below 5 ohms,unless otherwise specified
| Is This Answer Correct ? | 9 Yes | 5 No |
Answer / raj kumar
for large power s/s =.5
for small sub s/s =2.0
for domestic = 5.0
| Is This Answer Correct ? | 9 Yes | 5 No |
Answer / d m chudasama
it depends upon eath compositon. But shoud be normally less then 5 ohms.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / rajkumar.d
There is a good deal of confusion as to what constitutes a
good ground and what the ground resistance value needs to
be. Ideally a ground should be of zero ohms resistance.
There is not one standard ground resistance threshold that
is recognized by all agencies. However, the NFPA and IEEE
have recom- mended a ground resistance value of 5.0 ohms or
less.
The NEC has stated to “Make sure that system impedance to
ground is less than 25 ohms specified in NEC 250.56. In
facilities with sen- sitive equipment it should be 5.0 ohms
or less.”
| Is This Answer Correct ? | 0 Yes | 0 No |
how many maximum nos of add on contact we shd provide on 4 no contactor
what is static electricity and how it generates?
If the circuit breaker will not close or it will trip, what will you do?
why should we have to maintain pf in our site 0.9????????
why are laminations used in constructing the field core?
The temperature rise in the sys, which leads to ….. a) Increases stress& length b) increases stress but decreases length c) Decreases stress & increase length d) decrease stress & length
1 Answers Engineers India Limited,
We use MCCB not MCB for motor starters because MCCBs has capablity to drawout the motor starting current which is 5-6 times the full load current of motor for 1sec. Then why we use SDF in starter panel means MCC panels. Pls reply if any one knows this answer.
why we used dc supply for field in dg set
0 Answers Hindusthan National Glass,
Why HT voltages are expressed in 11KV,22KV,33KV and so on? (ie in times of 11)
which is batter in construction job,ELCB or RCCB?
What is a captive power plant?
what is a bus post insulator? explain its application in a substation.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)