What is the permissible value of earth resistance!
Answers were Sorted based on User's Feedback
Answer / rkshjangra
For large power station = 0.5
for small substation = 2.0
for domestic wiring = 5.0
| Is This Answer Correct ? | 36 Yes | 4 No |
Answer / p.gupta.1852
Earth resistance should be as small as possible . It
depands on voltage level of the system to be grounded . As
voltage level increases the earth resistance required to be
nearer to zeero as far as possible . Earth resistance
should not exceed 5 ohm for 433V distribution system and
should be below 1 ohm for 66 KV Grid .
| Is This Answer Correct ? | 26 Yes | 4 No |
Answer / mahesh babu-calicut
the earthing resistance of any electrical system should be
below 5 ohms,unless otherwise specified
| Is This Answer Correct ? | 9 Yes | 5 No |
Answer / raj kumar
for large power s/s =.5
for small sub s/s =2.0
for domestic = 5.0
| Is This Answer Correct ? | 9 Yes | 5 No |
Answer / d m chudasama
it depends upon eath compositon. But shoud be normally less then 5 ohms.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / rajkumar.d
There is a good deal of confusion as to what constitutes a
good ground and what the ground resistance value needs to
be. Ideally a ground should be of zero ohms resistance.
There is not one standard ground resistance threshold that
is recognized by all agencies. However, the NFPA and IEEE
have recom- mended a ground resistance value of 5.0 ohms or
less.
The NEC has stated to “Make sure that system impedance to
ground is less than 25 ohms specified in NEC 250.56. In
facilities with sen- sitive equipment it should be 5.0 ohms
or less.”
| Is This Answer Correct ? | 0 Yes | 0 No |
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?
How do you reverse the direction of rotation of a FAN?
When we need start the motor by method of star delta which size (KW or HP)motor should must be operate in Star Delta Method,
i have done my b.tech in 2009 .still hunting for a job...wat shud i answer if intervevwr asks..(what u have done 1yr)
I am new guy as an electrical engr. in a 100MW HFO based power project. I am in operations division. I have noticed from last few days, my supervisor sends the last 24 hours energy generation calculation to my plant manager. I have noticed, he calculated last 24 hour's generated energy differences in KWH then he multiplied it with a multiplying factor 960. for example: total difference =2.685 KWH*960= 2577.6 MWH. but he does not not know what is multiplying factor 960?? can anybody explain it??
Abb 11kv how it is closing automatically when the cb is racking in and rack out when it reaching test position
What is LSIG ?
what are types of ups?
if v r considering a 4000/1A ct,if v inject 1 amps in secondary core wat happens?(consider as 2 core ct,each for metering and protection)
Define over current & earth fault ?how its functioning ?
what is the surge arrestor?how it operates?what is the range for it?
Why voltge arev transformed in to 132KV/66/KV/33KV like that
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)