Why 11KV/440V distribution supply use for Domestic use?
Answers were Sorted based on User's Feedback
Answer / arti
11kV is the transmitted voltage. Voltage is usually
transmitted at higher voltage so as to save the cost of
copper (conductor side).
All the domestic appliances as per Indian standards are
rated at 250V and P-N voltage tapped from a phase of 3-
phase 440V is 250V (440/ sqrt(3)) approx. So 11kV/440V is
used for distribution suply.
| Is This Answer Correct ? | 54 Yes | 5 No |
Answer / sathish
This stage is called as secondary distrbution in this stage they convert ffom 3 wire to 4 wire system. In domestic we need l-n or r-y-b-n
| Is This Answer Correct ? | 9 Yes | 10 No |
Answer / yasuteru
because domestic appliances work on low voltages
| Is This Answer Correct ? | 0 Yes | 6 No |
PLZ EXPLIN ABOUT CLASS PS CLASS CT .WHY THEY R DESINED AND FOR WHAT PURPOSE?WHY OTHER CT CANT BE USED AS PS CLASS CT? EXPLAIN IN SIMPLE LAUNGAGE IF POSSIBLE PLZ GIVE CIRCIT DIAGRAM?EMAIL-RAJ_SINGH_0376@SIFY.COM
How to calculate the breaking capacity(like 15ka,20ka) of Circuit breaker (MCB,MCCB,ACB)
9 Answers Career Excellent Sdn Bhd, Neona, Northern Max Engineering, Sps Renewables, Terasaki, UEM,
Why do not we prefer non conventional sources of energy to conventional sources?
how to determine kilowatts (real power) is used in energy meter? is it apparent power effect the disk rotation?
what irequirment need to be followed when working on live equipment
why we step down voltage level from 33kv to 11kv and 11kv to 415v.Instead we can step down voltage from 33kv to 415v directly using single transformer?
how to calculate KA rating of C.B?explain with Formula.
what is the difference between transformer and amplifier ??
Please let me know when replacing electromechanical Relays for protection of generators with sr489 multilin Relay, then there is no need to use 86 master trip relay Too. I am wondering this multilin relay has no contact to Stop breaker reclosing as 86 does
is there or does RCCB work for single phase connection?
how the length effects the ampacity of the cable? if a cable is carrying a current of 100A for 50m length then what will the effect on current if we double the length?
what is the purpose for open delta connection in potential transformer
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)