Suppose you using Float/ displacer type of level switch.
Do the followings:
1. Fill the process into chamber of level switching mark.
2. Contacts of level switch should be changed.
3. If already, closed contacts, then should change to open condition.
4. If contacts not changing, do the knob of switch to change.
Suppose you can not fill process into chamber.(Process may harmful, like ammonia etc).
1. Note the process specific gravity. Suppose it is 0.67.
2. Your height for level switching is 1000 mm.
3. Use water to fill into chamber for calibration instead of process.
4. 1000 x 0.67 = 670 mm
5. So fill into chamber up to 670 mm water. It will operate the switch.
aftabmazari@yahoo.com
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / mahalingam
The switches all are working in Digital mode.Like 0 or 1. To do the calibration confirm the NO & NC. Basically it is NC when the process reaches the desired level then the circuit will be NO.
| Is This Answer Correct ? | 0 Yes | 2 No |
what is the difference between Cv and air consumption? why the customer needs Air consumption details?
Q- Why Phase tester is only used for checking AC not DC ?
what is an ambient temperature?
Name and describe at least 4 status indicators, typically found on a PLC
what is the deluge ? How can its working?
what is span adjusment of transmitter? what is the function of positioner/
what u mean by speed control in turbin? how it was working?
How to work togather like sov,limit switch,proxy switch and booster in xv
generally for transmitter we are giving supply 24vlts?but we are getting output 4-20ma ? how it is possible? is there any operation inside the tx?pls give complete information?
I work on a electronic positioner transmitter 4211 at the field.I connect my multimeter in series to get the current output then I calibrate it to 4ma in 0% of position of the valve and 20ma in 100% position of the valve.My problem is in the field I get the correct output current based on my multimeter but in the dcs they only receive 40% in a output 20ma of this positioner.Then I try to simulate in this analog card and they receive the equivalent percent on the value that I simulated.Is ther any possibility to reset the zero and span of this positioner 4211 fisher.And what other possibility I can do to fixed this.This is my email add ( landicho_randy@yahoo.com )
What is TMR
whey we conect ammeter in series and voltmeter in parallel in circuit
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)