Suppose you using Float/ displacer type of level switch.
Do the followings:
1. Fill the process into chamber of level switching mark.
2. Contacts of level switch should be changed.
3. If already, closed contacts, then should change to open condition.
4. If contacts not changing, do the knob of switch to change.
Suppose you can not fill process into chamber.(Process may harmful, like ammonia etc).
1. Note the process specific gravity. Suppose it is 0.67.
2. Your height for level switching is 1000 mm.
3. Use water to fill into chamber for calibration instead of process.
4. 1000 x 0.67 = 670 mm
5. So fill into chamber up to 670 mm water. It will operate the switch.
aftabmazari@yahoo.com
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / mahalingam
The switches all are working in Digital mode.Like 0 or 1. To do the calibration confirm the NO & NC. Basically it is NC when the process reaches the desired level then the circuit will be NO.
| Is This Answer Correct ? | 0 Yes | 2 No |
WHAT IS D/O D/I AND A/O A/I PLZ EXPLAIN
all types of liquid analyzer principle with drawing?
WHAT ARE THE INSTRUMENTAL DIAGRAMSOF VALVES?
0 Answers Artikal, ITC Infotech,
why we use 4-20 mA for calibration of the instruments.why we cant use 0-20 mA?
What are continuances of connecting earthing and shield of branch cables (instrument to Junction box), at the same earthing pot provided on JB? Is it ok, or may produce some problem?
0 Answers Process Control Technologies,
why the discharge pressure of ID fan showing negative at fan running condition.(boiler operating condition.)
If the on Of the DO module is off in the System cabinet, then what is the Procedure to check weather the Module is working or not.
difference between plc and dcs?
how we can calibrate split range control valve?
In most process, speed of motor controlled by control system with a reference pot . Now if i start & it becomes uncontrollable, i.e.gets directly start & stop after certain time.Then which reasons can make such problem? can motor may be faulty?how?
WHAT IS THE VALUE OF MICRON
wht is loops ? how many loops are there?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)