why we use 4-20 mA for calibration of the instruments.why
we cant use 0-20 mA?
Answers were Sorted based on User's Feedback
Answer / naveen
Logically Zero milli amps means no current in the circuit .
if we have an initial value to be measured , we cant measure
it as zero milli amps . It means no current in the circuit
or the circuit is open . so we go for the span of 4 to 20 mA
. this is coz we can easily split 4- 20 as multiples of four
(4,8,12,16) which means 0%,25%,50%,75%and 100% respectively.
| Is This Answer Correct ? | 24 Yes | 4 No |
Answer / sanjay sojitra
The live-zero represented by 4 mA allows the receiving
instrument to detect some failures of the loop, and also
allows transmitter devices to be powered by the same
current loop (called two-wire transmitters)
| Is This Answer Correct ? | 15 Yes | 2 No |
Answer / nirmalya basu
In both of the measurement 20ma represents full data and 4ma
or 0ma shows no data.But with 0ma we cant diagnose the wire
breakage in the transmission line but with 4ma we can diagnose
because if this type of fault is occurred then it shows
0ma.Thats why 4 20ma is used.
| Is This Answer Correct ? | 8 Yes | 0 No |
Answer / vikash tiwari
4-20ma is a linear system.
Live zero system used in loop so 4-20ma use.
Various instrument use in a loop,when one instrument is faulty so not required to check all loop instrument in live zero system.
| Is This Answer Correct ? | 0 Yes | 0 No |
can we connect instrument earth pit to electrical earth pit, if not why?
How can measure flow in oil line?which type of transmitter is generally used?
What is difference between Isolator and Barrier ?
what is PM/CM/RCM?
what is function of switch, and how is it work, explain with difination
0 Answers Bapco Bahrain Petroleum Company,
What is the input impedence of an OPAMP as an ideal device.
why are set -10vdc in bently neveda vibration system.
if conical type tank in top LEFT side solid material coming but LT MOUNTED IN TOP OF LEFT SIDE, how to measure ultrasonic level transmitter ?
what are the problem's will accure in dcs or plc hadware and what are the solution for it?
Explain Split Range Control In Control Valve Briefly.
generally transmitter power supply having some range(12v to 35v) but the out put(4-20 mA) must same for given input.If we vary the power supply voltage then output mA also to be change according to V=IR. Is there any voltage regulator in the transmitter ?
Why MUX JB's are using only Temperature Element in Fundation field bus?
0 Answers Reliance Industries,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)