why we use 4-20 mA for calibration of the instruments.why
we cant use 0-20 mA?
Answers were Sorted based on User's Feedback
Answer / naveen
Logically Zero milli amps means no current in the circuit .
if we have an initial value to be measured , we cant measure
it as zero milli amps . It means no current in the circuit
or the circuit is open . so we go for the span of 4 to 20 mA
. this is coz we can easily split 4- 20 as multiples of four
(4,8,12,16) which means 0%,25%,50%,75%and 100% respectively.
| Is This Answer Correct ? | 24 Yes | 4 No |
Answer / sanjay sojitra
The live-zero represented by 4 mA allows the receiving
instrument to detect some failures of the loop, and also
allows transmitter devices to be powered by the same
current loop (called two-wire transmitters)
| Is This Answer Correct ? | 15 Yes | 2 No |
Answer / nirmalya basu
In both of the measurement 20ma represents full data and 4ma
or 0ma shows no data.But with 0ma we cant diagnose the wire
breakage in the transmission line but with 4ma we can diagnose
because if this type of fault is occurred then it shows
0ma.Thats why 4 20ma is used.
| Is This Answer Correct ? | 8 Yes | 0 No |
Answer / vikash tiwari
4-20ma is a linear system.
Live zero system used in loop so 4-20ma use.
Various instrument use in a loop,when one instrument is faulty so not required to check all loop instrument in live zero system.
| Is This Answer Correct ? | 0 Yes | 0 No |
State bernoulli’s application.
how to calculate density?
What is a PID controller and how can it to applied to our everyday life?
Tell me the field calibration procedure step by step with diagram of pressure gauge, pressure switch, pressure transmitter, temperature switch, level switch, flow switch, flow transmitter.
What is shielding effect?
0 Answers Process Control Technologies,
difference between vaccum and draft
what is Instrument Schedule, and what it is mainly used for?
What safety precautions you will adopt to work on Steam service control valve?
What is the use of control cable?
why use to 250 ohm for hart protocol and why hart communicator not communicate without 250 ohm
define COMPENSATION??
Please any one can explain how to calibrate transmitter (smart) online with out remove from the container suppose it is interface level or static pressure level measurement we dont want to remove transmitter from the container mean it is running plant please give me detail. thankx brothers
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)