Answer / naveen
Logically Zero milli amps means no current in the circuit .
if we have an initial value to be measured , we cant measure
it as zero milli amps . It means no current in the circuit
or the circuit is open . so we go for the span of 4 to 20 mA
. this is coz we can easily split 4- 20 as multiples of four
(4,8,12,16) which means 0%,25%,50%,75%and 100% respectively.
| Is This Answer Correct ? | 24 Yes | 4 No |
Answer / sanjay sojitra
The live-zero represented by 4 mA allows the receiving
instrument to detect some failures of the loop, and also
allows transmitter devices to be powered by the same
current loop (called two-wire transmitters)
| Is This Answer Correct ? | 15 Yes | 2 No |
Answer / nirmalya basu
In both of the measurement 20ma represents full data and 4ma
or 0ma shows no data.But with 0ma we cant diagnose the wire
breakage in the transmission line but with 4ma we can diagnose
because if this type of fault is occurred then it shows
0ma.Thats why 4 20ma is used.
| Is This Answer Correct ? | 8 Yes | 0 No |
Answer / vikash tiwari
4-20ma is a linear system.
Live zero system used in loop so 4-20ma use.
Various instrument use in a loop,when one instrument is faulty so not required to check all loop instrument in live zero system.
| Is This Answer Correct ? | 0 Yes | 0 No |
what is Green field /brown field exposure in chemicals /oil /petrochemicals /refineries /paints /speciality chemicals /gas /FMCG /glass industry
Which are all the commonly used Bordon tubes in the pressure gauges. Do any one use ASTM A 312 tubes for this purpose?
Pl send the model question paper of mahagenco account officer post
Why we used cage in control valve?
where uses EXe /EXd/Exo/Exn/Exp/Exq/EXia
What is the purpose of MATLAB?
Why is the orifice tab provided?
Reason for capillary type dp level transmitter fluctuation
How can we say that accuracy of measurement increases by using 3 or 4 wire RTD? because for example: If resistance of RTD element is say r ohms and Resistance of the cable from transmitter to RTD is R ohms And if 4 wire RTD is used, ____._____________________ R ohms | |_____._____________________ R ohms / \ / r ohms \ \ | |______.__________________ R Ohms | |_______._________________ R ohms Then the actual resistance measured will be: Total = r + R/2 + R/2 = r +R Ohms Note: r+R instead of r ohms. hence error
Explain the difference between plc and cnc?
1)how can calibrate temperature transmitter? 2)how can calibrate flow transmitter? 3)how can calibrate level transmitter?
3 Answers ccic, Emerson, JK Pharma, NIGC, Rockwell, UltraTech,
if conical type tank in top LEFT side solid material coming but LT MOUNTED IN TOP OF LEFT SIDE, how to measure ultrasonic level transmitter ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)