Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


how we can calibrate split range control valve?



how we can calibrate split range control valve?..

Answer / sam

Below is a previous discussion on the subject. In your
question you do not give enough detail so I cannot give a
more detailed answer than below.
If you need more detail post a new question with more detail
about your application like valves where and how installed,
valve, actuator and line sizes, type of positioners, process
details ext. Also note that split range is done on two valve
installed in parallel in the same line and not just one as
in your question.



Question
Explain Split Range Control In Control Valve Briefly.
Question Submitted By :: Jaydeep_6494u I also faced this
Question!! Rank Answer Posted By Re: Explain Split
Range Control In Control Valve Briefly. Answer
# 1
split range control is which the output of a controller is
split to two or more control valves. For eg,
For 0% controller output,valve A fully open & B fully
closed.
For 25%, Valve A 75% open,B 25% open
For 50%, Valve A& B- 50% open,
For 75%, Valve A 25%open, B-75%open..
For 100%, Valve A fully closed & valve B Fully Open..

Like this, d controller output action can be set depending
upon the application...

Is This Answer Correct ? 5 Yes
1 No

0
Arunnatraj
Re: Explain Split Range Control In Control Valve
Briefly. Answer
# 2
In addition wt ANS.1-
in split range control the control signal is split in two
ranges according to the application .for eg,4-20MA.signal
can be used as 4-12 MA. FOR VALVE A OPEN i.e.50%.& 12-20MA
for vlv b open.vice-versa.

Is This Answer Correct ? 4 Yes
0 No

0
Nilesh Karpe



Re: Explain Split Range Control In Control Valve
Briefly. Answer
# 3
Split range is as per answer 2 and not answer 1. Answer 1 is
using two valves, one is a fail open and one is a fail
close. The 4 to 20mA control signal is then controlling the
two valves but in opposite directions. This can also be done
by calibrating the one positioner as a direct acting and the
other as a reverse acting.
Yes this is 100% correct and can be done and the two valves
will work perfectly and in exactly opposite directions to
each other. In a case like this the two valves will have to
be identical as well otherwise the balancing act you are
trying to perform with this setup might not work.
Never seen a application where you would need this but if it
needs to work like that, it can be done.

Split range means you are splitting a 4 to 20mA control
signal in two.

This is very useful in applications where the product flow
increases very rapidly and then falls away again. a Good
example will be before a slug catcher where the incoming
product from the well heads is coming in suddenly very fast
and then falls away again after a couple of minutes.
Another application is to control the steam from a boiler.
At times you need a lot of steam and other times you only
need a small amount.
How do you size the valve needed to control these very big
changes. a Small valve is needed to control the normal flow
but if the flow increases the small valve will open fully
and it will still be to small to control the now very high
flow or pressure. If you install a big valve to control the
big pressure or flow the valve will only open 2 to 5% most
of the time and it will be impossible to do stable control
with such a valve opening. Say nothing about the plug and
seat that will only last a couple of days.
To control these very high variance in flow and pressures of
the process we install two valves in parallel in the same
line. Normally the one is a small valve and the other is
about twice the size of the small valve.
The design and process engineers will decide what minimum,
normal and maximum conditions are and do the valve sizing
accordingly.
We calibrate the small valve to open from fully close to
fully open with a signal of 4 to 12 mA. We then calibrate
the second bigger valve to open from fully close to full
open with a signal of 12 to 20 mA.

In a situation where you use identical valves you can take
the signal from one controller and send it to both valves
but in the above application it is better to use two
controller but with the same input from one pressure or flow
transmitter. Each valve will then be controlled individually
from its own controller and on it's own PID tuning set. I am
sure you can see that it will be quite impossible to find a
PID tuning set that are appropriate for both the big and the
small valve and it is therefore better to use two
controllers but with the same input.

During normal operations the small valve will control the
process without any problems based on the input from the
pressure or flow transmitter, and the bigger valve stays
close all the time. If the process changes to something
bigger than what the small valve can handle the second
bigger valve needs to help, and will start opening up, once
the small valve is fully open. Once the demand falls away
the big valve will start to close and then the smaller valve
until the process is back to normal operating conditions..
Both valves receive a full 4 to 20mA signal from it's own
controller, but will only react based on the 4 to 12 or 12
to 20mA calibration that was done on each valve's positioner.

In other simpler applications you can use two identical
vales and set their positioners as above and send the one
controller output signal to both. One PID tuning set will
also work for both valves and conditions.

The valve sizes will depend on what the conditions are so
they can be the same or they might need to be different sizes.
Good luck

Is This Answer Correct ?    4 Yes 2 No

Post New Answer

More Instrumentation Interview Questions

generally transmitter power supply having some range(12v to 35v) but the out put(4-20 mA) must same for given input.If we vary the power supply voltage then output mA also to be change according to V=IR. Is there any voltage regulator in the transmitter ?

1 Answers  


how can we calibate ph meter. how can we calibrat conductivimeter how can we calibrat massflowmeter & it s working.

1 Answers  


What is the expansion of RADAR? How it works?

7 Answers   RasGas,


How does work A temperature valve or fv control valve in process plz brief me

0 Answers   Jindal,


what is difference between E/P positioner and I/P positioner. Why E/P fixed in below actuator and why I/P fixed in other place

1 Answers  


WHAT IS THE DIFFERENCE B/W PLC and DCS

10 Answers   Bhel,


Hello-I know this not an engineering question,I am working in gulf & i want to do correspondence diploma in instrumentation,can any one give me the address of any university in which this courses are available.

2 Answers  


i have used level transmitter in starch cooking preparation tank. tank total height 2mtr.sometime LT display shows some error value when tank is fully empty and diaphragm side i already checked okay no problem in diaphragm area. field cable checked 24volt and mA shows correct value while tank empty mA is 4mA. 4mA i needed that 0% but display showing 10% or 15% percentage values are varying continously please give any good solution for me.....

0 Answers  


pl give the guidance for DUBAL written test

1 Answers  


Working principle capacitance type level transmitter

3 Answers  


installation process of orifice,a question asked for confusion creation in interview by BARC 1.if orifice is tightly fitted with pipe ,it will act like venturi 2.if orifice is left hanging in between liquid it will not create the pressure difference exactly,

0 Answers   BARC,


pt range is -45 psi to 45 psi.friends can you give answer with calculation and with linerity scale like 0%,25%,50%,75%& 100%?

1 Answers   WB,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)