What should be the overcurrent, instantaneous overcurrent, short cicuit
current settings (i.e. how many times of motor full load and what is the time
duration) for a motor?
Answer / harit
Overcurrent setting should be 120% of the Full Load Current of motor (time setting should be as per the recommendation of the manufacturer or Load characteristic)
instantaneous overcurrent & short circuit current settings should be 7 to 8 times of the full load current. Time interval to trip : should be set at zero (instantaneous).
| Is This Answer Correct ? | 0 Yes | 0 No |
what are trouble functions of transformer?ex. prv trip,oltc,oti,wti.explain detail.
cb used in railway applications is?
why three phase capacitor takes unbalanced current in capacitor bank?
what will happen if one of the phases from a 3-phase motor is disconnected?? stop/run at 2/3rd speed or run at same speed????
What is Procedure the procedure to select CT's & PT's in 66kV and above substation
what is oti and wti
what is difference between VAT & CST
why maintenance batteries used in DG sets not in MAintenance free Batteries.
in transformers for ex. 100mva and 400kv the secondary current is about 420 amps but for selection of bushing the capacity of selected bushing is 2000A why there is such big difference ?
what is a circuit breaker. Weite the types of circuit breaker.
What is the difference between multimeter
what is range ACB
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)