There are two nos of 33Kv/11Kv 5MVA transformers conecting
through HT cable from substation having metering at
substation itself.One transformer used at a time another
remains stand by.Further 11 nos of 11Kv/440V transformers
are attached on it and each transformer is having its own
Power factor correction panel.Now one 33/11Kv transformer
at no load condition/Stand by condition is having power
factor in leading side upto 0.21 and while when another
tranformer at same situation have power factor in lagging
0.42. Now one thing is clear that transformer one is having
1.5 Km long 33kv cable due to that PF goes in leading side
and another is having only 250 mtr length remains him
lagging. Now i want to know that how i can maintain the
Power factor at no load/ stand by position though both are
behaving in seperate manner.
Answer / k.prakashchandra
Pf at no load is not to be heeded ,as the magnetizing
current is very low and the ct may not measure it accurately
wrt both magnitude and angle shift
Is This Answer Correct ? | 4 Yes | 2 No |
what is mind in cable
lightning arrester rating selection procedure: (line to line voltage(kV)/(squ.root of 3))*squ.root of 2. now the question is, IS this above formula correct for both STAR and DELTA connected system???
Railway Basic electrical engg technical question with answer
why is the transmission voltage is multiple of 11?
What is the principle of residual protection?
What is relation bet kvar & microfarad
is ac supply can store
when we decide to use soft starter drive or vfd drive in mcc to operate apump?
how will u exactly calculate the unit consumption of the Air conditioners?Split/Window/
i want to know about psu exam eligibility critaria?
which plant has high load factor
What effect does a very low impedance have on the Voltage regulation? On the short-circuit current?