When we change the tap position of 10MVA transformer it
suddenly tripped with Out of step indication and also with
Static differential relay indication, Transformer Bucholz
relay indn and Low oil level indication. Before 1 week the
same problem occured by changing the tap position. but at
that time only oltc bucholz relay activated. After testing
the TxR Relay team & PET team cant find any solid reason.
The values are ok also. So plz answer wat's the reason for
this incident? anybody plz help.
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
OLTC has contact switches on rotating spindle and diverter
switch. Bucholtz relay acts as the oil is burnt in the
chamber due to arcing caused by loose contact .The spring
tension of the switches are to be checked for correct
tightness.If the contact is not correct ,the differential
relay may also act due to imbalance of currents.Do not
operate OLTC till the fault is set right.And the oil may
have to reconditioned.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / k.prakashchandra
There is a loose connection in one of the phases of OLTC
contacts.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / priyanka
Problem seems to be around the OLTC. More than 70% of
problems in transformer are due to OLTC.
Get your OLTC motor checked,surely you can find the
tripping reason there. Now about the tripping indications
following is the possibility-
Out of step - OLTC is a kind of stepper motor, when you
change the tap position the motor moves at a particular
step angle. In case your motor is faulty, it will move out
of step leading to frequent sparking across contacts
(Buccholz indication) and current imbalance due to improper
step angle (static differential).
Low oil level indication has no link with this, it simply
shows that conservator level is down.
| Is This Answer Correct ? | 0 Yes | 0 No |
list the advantages of RCCB over other circuit breakers?
Can anybody explain Why starters are not used for motor starting in industries?
WHY STABILIZER SHOULD USED
What is lighting kitts.
In generation,transmission and distribution voltage frequency is either 50HZ or 60 HZ;why are only these frequencies?
3- What is the target from Zero Impedance, Single Phase Imp., S/C Imp. and magnetic balance tests?
two 100W/230V bulb are connected in series. what would be the voltage drop across 1 bulb
which motor is used in mixies
why generally transformer are in star to delta
can we coorect P.F. OF 320 KVA ALTERNATOR AT LOCAL SITE WITH RATED .8 PF LAGGING.
i have flexible wire. size of conductors is 0.190 mm & no.of conductors are 48. then size of wire comes 1.37 sqmm instead of 1.5 sqmm . the what is tolerance for this size.
WHY DOES NEUTRAL DO NOT CARRY EVEN THOUGH IT CARRIES RETURN CURRENT?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)