When we change the tap position of 10MVA transformer it
suddenly tripped with Out of step indication and also with
Static differential relay indication, Transformer Bucholz
relay indn and Low oil level indication. Before 1 week the
same problem occured by changing the tap position. but at
that time only oltc bucholz relay activated. After testing
the TxR Relay team & PET team cant find any solid reason.
The values are ok also. So plz answer wat's the reason for
this incident? anybody plz help.
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
OLTC has contact switches on rotating spindle and diverter
switch. Bucholtz relay acts as the oil is burnt in the
chamber due to arcing caused by loose contact .The spring
tension of the switches are to be checked for correct
tightness.If the contact is not correct ,the differential
relay may also act due to imbalance of currents.Do not
operate OLTC till the fault is set right.And the oil may
have to reconditioned.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / k.prakashchandra
There is a loose connection in one of the phases of OLTC
contacts.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / priyanka
Problem seems to be around the OLTC. More than 70% of
problems in transformer are due to OLTC.
Get your OLTC motor checked,surely you can find the
tripping reason there. Now about the tripping indications
following is the possibility-
Out of step - OLTC is a kind of stepper motor, when you
change the tap position the motor moves at a particular
step angle. In case your motor is faulty, it will move out
of step leading to frequent sparking across contacts
(Buccholz indication) and current imbalance due to improper
step angle (static differential).
Low oil level indication has no link with this, it simply
shows that conservator level is down.
| Is This Answer Correct ? | 0 Yes | 0 No |
what is Real power and Reactive power ? what is difference between them ?
My energy meter ratio is -/110/root 3,1A and connected line CT is 100/1,PT is 11kv/110 so what is the MF for meter
what will be the minimum megger value for 132 Kv (earthed) potential transformer
which type of breaker sould be used for different level of voltage ? (i.e at 11 Kv, 33 Kv, 66 Kv....
how does high earth to neutral voltage affects electronic circuit?
GIVE CONDITION FOR MAX EFFICIENCY OF 3-PH TRANSFORMER AND D.C MOTOR
what will happen if capacitor bank is used in generation side?
- two pumps must work with them at the same time but if the first pump start the second pump must delayed for some time to start also , with motor rated power = 90 KW and rated voltage = 380 V and rated power factor = 0.85 lag please draw the power and control circuit for it and determine all circuit components parameters that you use it
phase clearance between phase to phase and earth
how to calculate a cable size while load is given in amp or kw and length is also define.?
If a rotary UPS is in line through grid power; What would be the impact on Power Factor if the load through rotary ups is 25% , 50% , 75% & 100%. Will the power factor reduce with less load?
how give earthing conection to household equipment?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)