Good Evening all.My question is - For a feed water line to
an equipment if i need to measure the flow we will use
orifice /magnetic/vortex depend on cost/spec.If i need to
measure a ''Alarm''signal and ''Interlock'' from one point
i think we can use orifice type in one location with 2
different tapping points - one for alarm and one for an
interlock to flow valve..If in case i need to have both
these signals(Alarm & interlock) from magnetic flow
meter,is it possible??will 2 seperate sensors will be
located inbuilt r we can program it ??..i thk we can have
one transmitter with these 2 signals...need to know any
technical issues are there?pls clarify
Answers were Sorted based on User's Feedback
Answer / carl_ellis
If this is not SIS (safety instrumented), the 4-20mA from a
single flow transmitter can feed a separate I/O modules (4-
20in, relay out) an alarm module and a separate interlock
module.
Or, depending on the converter/transmitter model, most
magmeters have at least one assignable relay output, some
have two relay outputs.
I've always used orifice flange unions that have only one
set of taps. There might be a double tap flange unions, or
I suppose you can drill and weld the pipe for taps. But
again, unless this is SIS, why would you? Decisions made
on a 4-20mA flow signal on a PLC?DCS/Controller/I?O modules
can do multiple functions.
If your situation is SIS, you should state that.
Carl Ellis
Measure First
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / carl_ellis
It seems you are using a flow meter's relay(s) to generate
alarm signals at various amplitudes: low, low/low, hi,
hi/hi.
The flow meter doesn't really use these alarm signals
itself, rather it generates the alarm signals and provides
the alarm signals to other devices, for whatever purpose,
alarm, annunciation or an interlock.
There might be a flow meter with 3 alarm relays. I don't
know. That's a shopping issue.
Most places will use a PLC, a controller or a DCS to
generate alarms from the analog flow signal.
But if your flowmeter doesn't have enough relays, then use
a "DC alarm trip" I/O module with the flow meter's 4-20mA
analog output.
The modules have an analog input and one or two relay
outputs with adjustable setpoints. There's probably a
dozen models on this page:
http://www.api-usa.com/signalconditioners_alarms.php
These I/O modules are not used "in a magmeter", they're
external I/O modules.
They place a small burden resistance in the 4-20mA circuit,
need an enclosure and AC or DC power to operate, but they
accomplish the task of providing multiple alarms at various
setpoints.
The 4-20mA signal is wired in series with the I/O module
and any other receiver devices.
Carl Ellis
Measure First
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / thiagaraj
@CARL ELLIS.. Thanks for your response.In case of using
Alarm (or) Interlock it was a normal practise that we
use ''LOW''LOWLOW'' (OR) ''HIGH''HIGHHIGH'' signal in the
same instrument(orifice etc)..If i need to
use ''LOW''HIGH''LOWLOW'' in the same Instrument is it
possible to use these 3 alarms in a single instrument(flow
transmitter )..If yes is it can be used in Magnetic flow
meter ..pls state its advantages and disadv also.pls clarify
Is This Answer Correct ? | 0 Yes | 1 No |
Difference HAZOP and HIRA
Question on maha cement
What is MLFB number for Siemens?N How they are defined?Give me Answer with example like take any Signal module....
What should be the main consideration while starting the Rotating compressor when we dont know the cut in and the cut off pressure setting of the pressure switch
why direct mounted pressure transmitters is always installed with DBB ( double bleed block) valve in process line or top of the tanks ?
A pressure differential gauge type of instrument has a manifold with 2 isolation valves (hp and lp),2 vents(1 each for hp and lp) and 1 equalizing valve. Determine the position of each valve(either fully closed or fully open) when troboulshooting to: 1. zero the transmitter. 2. determine if there is a block in the impulse line. 3. determine if the gauge is functioning properly. The process fluid is water.
uses of profibus?
How many are the types of instrument cables in terms of No. of pair.
What is basic of instrumentation
what is the difference between dcs & plc
Boolean algebra
How to calibrate DP tramitter in flow measurement application? consider my range of flow is 0 to 2000 kg/hr ? please give calculation of , How much pressure applied on low pressure side and high pressure side please give detail of calculation .... It so important for me please reply as soon as possible