Good Evening all.My question is - For a feed water line to
an equipment if i need to measure the flow we will use
orifice /magnetic/vortex depend on cost/spec.If i need to
measure a ''Alarm''signal and ''Interlock'' from one point
i think we can use orifice type in one location with 2
different tapping points - one for alarm and one for an
interlock to flow valve..If in case i need to have both
these signals(Alarm & interlock) from magnetic flow
meter,is it possible??will 2 seperate sensors will be
located inbuilt r we can program it ??..i thk we can have
one transmitter with these 2 signals...need to know any
technical issues are there?pls clarify
Answers were Sorted based on User's Feedback
Answer / carl_ellis
If this is not SIS (safety instrumented), the 4-20mA from a
single flow transmitter can feed a separate I/O modules (4-
20in, relay out) an alarm module and a separate interlock
module.
Or, depending on the converter/transmitter model, most
magmeters have at least one assignable relay output, some
have two relay outputs.
I've always used orifice flange unions that have only one
set of taps. There might be a double tap flange unions, or
I suppose you can drill and weld the pipe for taps. But
again, unless this is SIS, why would you? Decisions made
on a 4-20mA flow signal on a PLC?DCS/Controller/I?O modules
can do multiple functions.
If your situation is SIS, you should state that.
Carl Ellis
Measure First
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / carl_ellis
It seems you are using a flow meter's relay(s) to generate
alarm signals at various amplitudes: low, low/low, hi,
hi/hi.
The flow meter doesn't really use these alarm signals
itself, rather it generates the alarm signals and provides
the alarm signals to other devices, for whatever purpose,
alarm, annunciation or an interlock.
There might be a flow meter with 3 alarm relays. I don't
know. That's a shopping issue.
Most places will use a PLC, a controller or a DCS to
generate alarms from the analog flow signal.
But if your flowmeter doesn't have enough relays, then use
a "DC alarm trip" I/O module with the flow meter's 4-20mA
analog output.
The modules have an analog input and one or two relay
outputs with adjustable setpoints. There's probably a
dozen models on this page:
http://www.api-usa.com/signalconditioners_alarms.php
These I/O modules are not used "in a magmeter", they're
external I/O modules.
They place a small burden resistance in the 4-20mA circuit,
need an enclosure and AC or DC power to operate, but they
accomplish the task of providing multiple alarms at various
setpoints.
The 4-20mA signal is wired in series with the I/O module
and any other receiver devices.
Carl Ellis
Measure First
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / thiagaraj
@CARL ELLIS.. Thanks for your response.In case of using
Alarm (or) Interlock it was a normal practise that we
use ''LOW''LOWLOW'' (OR) ''HIGH''HIGHHIGH'' signal in the
same instrument(orifice etc)..If i need to
use ''LOW''HIGH''LOWLOW'' in the same Instrument is it
possible to use these 3 alarms in a single instrument(flow
transmitter )..If yes is it can be used in Magnetic flow
meter ..pls state its advantages and disadv also.pls clarify
| Is This Answer Correct ? | 0 Yes | 1 No |
What is mean by Adapter block and net block?
What is the difference between working pressure and calibration pressure of a control valve
what's meanning of 1250KVA and how to calculate with Volttage and Current. answer give with example.
What is the difference between dry contact and wet contact?
how the flow rate is measured from a pipe with the help of pressure?
What is wet leg condition and why is it used?
Flame scanner
what are the different types of terminal lugs used for wiring termination?
which type inter lock use in petrochemical refinery,and oil & gas?
A pressure transmitter with a range of 0-100 bar.The accuracy of the instrument is 1% of upper range value? The pressure indicating transmitter is showing the system pressure is 50 bar. b. When you include the error, what is the minimum possible pressure in our fuel gas system? i. 49.5 bar ii. 49 bar iii. 1 bar iv. 0.5 bar We want to change the filter cartridge. We must depressure the fuel gas system. c. After we depressure the system in preparation for maintenance, the transmitter displays a pressure of +0.1 bar. At this time, what is the possible range of pressures in our fuel system? i. +0.099 to +0.101 bar ii. 0 to +0.2 bar iii. -0.1 to +0.3 bar iv. -0.9 to +1.1 bar
we have a s-5 simense plc having op7 .recently on op7 showing error 1.plc not present 2. DB error frequently. can u have any solution . please send me.
Definition of reverse and acting controllers:
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)