Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


i have height of stem drum level 1000mm.how i calculate the
DP transmitter

Answers were Sorted based on User's Feedback



i have height of stem drum level 1000mm.how i calculate the DP transmitter..

Answer / aftab ahmed mazari

1. Never use any one one port of transmitter at boiler
point and other to atmosphere. Never. It will make a
serious accident and also transmitter will never work.
2. Connect Hi side of DP transmitter at bottom point of
outlet from boiler and LO side of DP tranmitter at top side
of boiler point.
3. Also use condensation bottle at lo side of tranmitter
(top side of boiler point)
4. Suppose transmitter is almost same level of bottom point.
Now there are two methods of calibration:
Method No. 1
a. Do not open valves of boilers side.(Very Important).
just open both hi to atmosphere and fill water at low side
from top of dp transmitter.
b. Transmitter will show less mA as compare to 4 mA.
Suppose its showing 2 mA. Tranmitter zero elevated. Get
adjust 4 mA from HART.
c. Your range is 1000 mm. Usually specific gravity of
boiler water under temperature and pressure is 0.45. (It
depends upon boiler pressure and temperature).
d. So get range = 1000 x 0.45 = 450 mm of H2O. It is that
type of transmitter which did its zero by HART.So adjust 20
mA by feeding pressure of 450 mm of H2O.
e. Get connect piping of transmitter to sensing lines and
put in service the transmitter.
Another method is, you want to calibrate it at work shop
without using HART.
a. Usually water specific density/gravity at upper side
after getting out from boiler drum and being condensated in
pipe of transmitter is 0.99.
4 mA = 1000 x 0.99 = 990 mm H2O
It will be written as - 990 mm H2O.
b. Give pressure at lower side of dp transmitter 990 mm H2O
and transmitter Hi side must be opened to atmosphere.
c. Get adjust transmitter 4 mA.
d. 20 mA range = 1000 x .45 = 450 mm H2O
e. Apply 450 mm H2O pressure at Hi side of transmitter and
adjust 20 mA signal from range knob. Remember not to
disconnect lo side pressure.
Suppose, you want to calibrate from lo side only.
a. At 990 mm of H2O low side = 4 mA
b. Decrease the pressure from 990 to 540 mm of H2O (990 -
450 = 540) from low side, you will get 20 mA.
Note: If you put transmitter hi side connected to boiler
and low side to atmmsphere, DP transmitter will burst.
Becareful.

aftabmazari@yahoo.com

Is This Answer Correct ?    7 Yes 1 No

i have height of stem drum level 1000mm.how i calculate the DP transmitter..

Answer / rajesh

firstly select dp transmitter .connect one port to level pipe . and one exposed to air . so it becomes atm air to pressure inside the steam drum . now after placing , calibrate it with level and now the transmitter will give direct reading of level .

Is This Answer Correct ?    0 Yes 7 No

Post New Answer

More Instrumentation Interview Questions

installation process of orifice,a question asked for confusion creation in interview by BARC 1.if orifice is tightly fitted with pipe ,it will act like venturi 2.if orifice is left hanging in between liquid it will not create the pressure difference exactly,

0 Answers   BARC,


how can calibrate transmitter online

2 Answers  


what is sil (safety integrity level

0 Answers   Essar,


Tell me the field calibration procedure step by step with diagram of temperature transmitter, temperature indicator, flow indicator, level indicator, control valve, thermocouple, pressure indicator (digital & analogue).

1 Answers  


what is the difference between scaler and vector drive

0 Answers   Jindal,


Explain, and give a real-world example of MODULATING control

1 Answers  


what is the difference between servo valve & proportional valve

1 Answers  


Introduce yourself which is not present in your biodata?

0 Answers   GAIL,


How do you identify between actual alarm and false alarm in a Temperature Transmitter in SCADA based Control System

0 Answers  


What is difference between “Fault Tolerant” & “Fault avoidance” PLC? Application where these system s are used?

0 Answers  


what is the pressure in the tank when its level of liquid is 1.5 meters when its total capacity is 2 meters

2 Answers   Engro,


what is function of PLC, and how is it work , explain with difination

1 Answers   Bapco Bahrain Petroleum Company,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)