i have height of stem drum level 1000mm.how i calculate the
DP transmitter
Answers were Sorted based on User's Feedback
1. Never use any one one port of transmitter at boiler
point and other to atmosphere. Never. It will make a
serious accident and also transmitter will never work.
2. Connect Hi side of DP transmitter at bottom point of
outlet from boiler and LO side of DP tranmitter at top side
of boiler point.
3. Also use condensation bottle at lo side of tranmitter
(top side of boiler point)
4. Suppose transmitter is almost same level of bottom point.
Now there are two methods of calibration:
Method No. 1
a. Do not open valves of boilers side.(Very Important).
just open both hi to atmosphere and fill water at low side
from top of dp transmitter.
b. Transmitter will show less mA as compare to 4 mA.
Suppose its showing 2 mA. Tranmitter zero elevated. Get
adjust 4 mA from HART.
c. Your range is 1000 mm. Usually specific gravity of
boiler water under temperature and pressure is 0.45. (It
depends upon boiler pressure and temperature).
d. So get range = 1000 x 0.45 = 450 mm of H2O. It is that
type of transmitter which did its zero by HART.So adjust 20
mA by feeding pressure of 450 mm of H2O.
e. Get connect piping of transmitter to sensing lines and
put in service the transmitter.
Another method is, you want to calibrate it at work shop
without using HART.
a. Usually water specific density/gravity at upper side
after getting out from boiler drum and being condensated in
pipe of transmitter is 0.99.
4 mA = 1000 x 0.99 = 990 mm H2O
It will be written as - 990 mm H2O.
b. Give pressure at lower side of dp transmitter 990 mm H2O
and transmitter Hi side must be opened to atmosphere.
c. Get adjust transmitter 4 mA.
d. 20 mA range = 1000 x .45 = 450 mm H2O
e. Apply 450 mm H2O pressure at Hi side of transmitter and
adjust 20 mA signal from range knob. Remember not to
disconnect lo side pressure.
Suppose, you want to calibrate from lo side only.
a. At 990 mm of H2O low side = 4 mA
b. Decrease the pressure from 990 to 540 mm of H2O (990 -
450 = 540) from low side, you will get 20 mA.
Note: If you put transmitter hi side connected to boiler
and low side to atmmsphere, DP transmitter will burst.
Becareful.
aftabmazari@yahoo.com
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / rajesh
firstly select dp transmitter .connect one port to level pipe . and one exposed to air . so it becomes atm air to pressure inside the steam drum . now after placing , calibrate it with level and now the transmitter will give direct reading of level .
Is This Answer Correct ? | 0 Yes | 7 No |
What is the difference between HMI and Scada?
in instrumentation why we are using 4-20mA , why not voltage ? if somebody design a instrument which works on voltage then can we use that instrument?
What is the standard height for stancion supports? and what is the standard mounting height for different transmitters?
WHAT IS THE DIFF BETWEEN FREQUENCY AND INTENSITY?HOW IT WORKS IN FLAME SCANNER ?
How to calibrate the control valve.
Why thermo wells are used? What materials are used in thermo wells?
Where are oxygen analysers installed in cfbc boilers? What are their usual readings?
Why thermo wells are used?
what master plc do?
I am new in work for 1 of our project we have some instrument in BOM including Pressure, Temp. and so on, I also noticed some objects like pressure switch process HOOK UP; which I don't know what does "HOOK UP" mean here.
If fire would be inside the plant which fire detector is to detected the fire.
what is a vortex flow meter,mass flow meter and electromagnetic flow meter.particular use of this.means in which condition particular meter is used.