i have height of stem drum level 1000mm.how i calculate the
DP transmitter
Answers were Sorted based on User's Feedback
1. Never use any one one port of transmitter at boiler
point and other to atmosphere. Never. It will make a
serious accident and also transmitter will never work.
2. Connect Hi side of DP transmitter at bottom point of
outlet from boiler and LO side of DP tranmitter at top side
of boiler point.
3. Also use condensation bottle at lo side of tranmitter
(top side of boiler point)
4. Suppose transmitter is almost same level of bottom point.
Now there are two methods of calibration:
Method No. 1
a. Do not open valves of boilers side.(Very Important).
just open both hi to atmosphere and fill water at low side
from top of dp transmitter.
b. Transmitter will show less mA as compare to 4 mA.
Suppose its showing 2 mA. Tranmitter zero elevated. Get
adjust 4 mA from HART.
c. Your range is 1000 mm. Usually specific gravity of
boiler water under temperature and pressure is 0.45. (It
depends upon boiler pressure and temperature).
d. So get range = 1000 x 0.45 = 450 mm of H2O. It is that
type of transmitter which did its zero by HART.So adjust 20
mA by feeding pressure of 450 mm of H2O.
e. Get connect piping of transmitter to sensing lines and
put in service the transmitter.
Another method is, you want to calibrate it at work shop
without using HART.
a. Usually water specific density/gravity at upper side
after getting out from boiler drum and being condensated in
pipe of transmitter is 0.99.
4 mA = 1000 x 0.99 = 990 mm H2O
It will be written as - 990 mm H2O.
b. Give pressure at lower side of dp transmitter 990 mm H2O
and transmitter Hi side must be opened to atmosphere.
c. Get adjust transmitter 4 mA.
d. 20 mA range = 1000 x .45 = 450 mm H2O
e. Apply 450 mm H2O pressure at Hi side of transmitter and
adjust 20 mA signal from range knob. Remember not to
disconnect lo side pressure.
Suppose, you want to calibrate from lo side only.
a. At 990 mm of H2O low side = 4 mA
b. Decrease the pressure from 990 to 540 mm of H2O (990 -
450 = 540) from low side, you will get 20 mA.
Note: If you put transmitter hi side connected to boiler
and low side to atmmsphere, DP transmitter will burst.
Becareful.
aftabmazari@yahoo.com
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / rajesh
firstly select dp transmitter .connect one port to level pipe . and one exposed to air . so it becomes atm air to pressure inside the steam drum . now after placing , calibrate it with level and now the transmitter will give direct reading of level .
| Is This Answer Correct ? | 0 Yes | 7 No |
what is interface level and how it is calibrate?
what is the Instrumentation?
Explain working principle of lvdt?
Area classification, Equipments, Gas groups, temperature classification, Ingress protection, Fire Extinguishers.
draw the block diagram of a level transmitter ?
0 Answers Hira Group, Samsung,
What are the charcterstics of a P&ID controller block for Governor speed raise or lower for a load sharing functionality between 4 Gas turbines in droop mode.
where Pirani gauges are uesd in case of pressure measurement?
State four different types of flow measurement.
what is actual drum level and compensated drum level?
How we will check whether the proximity, which we have is either NPN or PNP, if no data sheet or manual or any details is available to us ???
plz send me placement paper of ongc
1.what is the effect of vapour presuure in orifice plate flow measurement 2.which is more effective 2 pressure sensors or one single differential pressure sensor in orifice plate measurement 3.how to design a v/i converter and i/v converter 4.how many type of thermocouple are there 5.how many leads are there in thermocouple measurement 6.how pressure sensors are connected in level measurement in differential pressure method 7.what is the output of capacitive pressure sensor (ac or dc),how its o/p is signal charactarized 8.what is the physical meaning of discharge coeeficient,why it is calculated,orifice plate what is its value,why it is less than 1,Q at upstream is equal to or not equal to Q at downstream of orifice plate why?what is vena contracta in orifice plate 9.why rotameter is called variable area flowmeter,it can measure flow even if area is not varying,why it is made tapered 10.design a 10 bit counter ,which counter you will prefer 11.how to remove self heating error in RTD 12.which is more sensitive pt100 or pt50 13.why thermocouple are connected in parallel 14.what is lead contact error in RTD,how to avoid 15.what is P,PI,PID,PD controller,why there is no ID controller 16.what is override,split range,sequential,ratio,feedforward,cascade controller 17.why we moved from SR to JK and then JK to master slave JK flipflop,give correct reason 18.how to measure level of a closed container which contains vapour and liquid,remember no vapour gas should be leaked,so ultrasonic and capacitive is not an option,design another method 19.how to design horse race counter including sensors and signal conditioning element 20.what is bevelling
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)