Question: How to calculate flow of air bubbler type level transmiter? According hight and density?
I love this question because it deals with the understanding of how a bubbler works - flow is not the issue, pressure is.
The calculated value for a bubbler is NOT flow. The critical, calculated value for a bubbler is pressure, because the air/gas pressure in the bubbler tube is a direct representation of the head pressure of the liquid column; which in turn, can be interpreted as the level of the liquid column.
Measurements of head pressure are always done in units of water column (wc), inches of water column or mm of water column, because water column is universal everywhere in the world.
The column of liquid might not be water, it might be some chemical or solution whose specific gravity (density) is not the same as water. So to determine the level, the head pressure measurement of the air/gas pressure in the bubbler dip tube needs to be corrected by the specific gravity. Level = measurement (wc)/specific gravity
The flow rate of air/gas is typically just enough to create a constant stream of bubbles, proving that the air/gas column in the tube has sufficient pressure to overcome the liquid column head pressure. Flow rates regulated by a constant flow, differential relay range from 0.5-2.0 CFH (15 L/hr to 55 L/hr).
Carl Ellis
Measure First
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / madani
Suppose level to be measured is 02 meters from the datum line.Fill the vessel with service liquid of 02 meters
height and adjust the purge rotameter flow until Transmitter output reads 20 ma DC.
Is This Answer Correct ? | 0 Yes | 2 No |
1.what is controller proportional gain 2.what is the controller intergral action time. 3.A proportional plus derivative controller that has a proportional band of 20% and a derivative action time of 0.1 minutes. Construct the shape of the output waveform for the triangular input if the input rises and falls at the rate of 4 units per minute.
what is the difference b/w normal thermocouple and skin type thermocouple?
Transducer Input 0 to 230 v ac Output-0 to 10vdc Receiver Input 0 to 10 vdc and Output 4 to 20 ma How?
How will you calibrate an Absolute Pr.Transmitter of range 400mmHg absolute ?
How to Calibrate Level Troll in field
key exchanges in wpa,wpa2,tls
What is the DIfferences between SMART transmitters and PROFIBUS DP/PA Transmitters?
why 4ma show higher zero ? i have transmiter flow renge 0-1000 m3/h but 4 ma show in monitoring 200 m3/h and 20 ma show 1000 m3/h i want when 4ma show 0 m3/h and 20ma 1000m3/h
which is the best type to measure level of a Tank(water). Displacer or Differential Pressure method?
Hi i m B.E. In elect. & comm. I m workin in bio mass plant from 6 mnths as inst. Engg. but now i m in dept. Of operation as shift engg...which is best operation or inst. 4 me? M confusd..plz help and reply me..
what is the daily job of an instrument commissioning supervisor
Why boiler chimney area oxyden sensor fixing?