which relay is better , instantaneous or IDMT relay .
Answers were Sorted based on User's Feedback
Answer / karthik
for metering, protection all will be taken in one CT --only core will be varied in that CT
for measurement -1s1,1s2
for protection - 2s1,2s2
only one CT is used
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / biswaindu parida
In a substaion we use different ratio of CTs for different purposes. Such as 200/1 for metering 400/1 for another back up, 800/1 for protection like wise. So suppose if a fault comes say around of 1200A then the secoundary level current for different Cts will not be same.
Lets analyse them indivisually.
1) The 800/1 Ct will read it as 1.5A. For that we can simply use Over current relay and trip the breaker.
2) The 400/1 Ct will read it as 3A . here we can use IDMT relay.
As per its function it will sends trip command to the breaker as soon as possible...because here the time of trip is inversely proportional to the amount of fault current
3) But however in case of 200/1 CT, it will read it as 6A. If it is a metering CT then it should be protected 1st. because it has less saturation point as compared to protection or back up CT. So here we will use instantaneous relay so that it will trip suddenly when the fault current goes above some pre defined value.
| Is This Answer Correct ? | 0 Yes | 3 No |
define digital electronic
How to select the proper VSD to operate high inertial load
What core magnetic balance test of transformer? How to do this test in a three phase Star delta (star-LV, Delta-HV) transformer? How to measure and where to measure? thanks and regards Austin
22 Answers Neutech, Power Grid, TSSPDCL,
What is the technical difference between On delay timer and a Star delta timer?
why fault current always calculated for 1 seconds?
why neutral and earth should not be connected on 3 phase 440v/50c/s supply at consumer side. where as on 25kv/ac/50c/s railway traction substation neutral and earth will be connected and track at substation. and track will act as neutral and earth. Reasons for this is needed urgently
long form of CT
3 Answers MSETCL Maharashtra State Electricity Transmission Co Ltd,
Hi, i want to know is meant by power quality? How it can calculated ? How we can improve?
how can get electrical "c" licence.i am complited in DEEE.PASSING YEAR OF 1993.WORKING IN PVT COCERN LT LINE.PLEASE ADVISE ME .CELL NO 9994786021
What is static frequency control used in gas turbines
whose motors self starting synchronous or Induction motor?give fact reason why not self starting another mother
sir iam a 3rd yr eee student.no core company comes for recruitment to our college.my aim is to be placed in l and t.tell me the procedures.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)