which relay is better , instantaneous or IDMT relay .
Answers were Sorted based on User's Feedback
Answer / karthik
for metering, protection all will be taken in one CT --only core will be varied in that CT
for measurement -1s1,1s2
for protection - 2s1,2s2
only one CT is used
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / biswaindu parida
In a substaion we use different ratio of CTs for different purposes. Such as 200/1 for metering 400/1 for another back up, 800/1 for protection like wise. So suppose if a fault comes say around of 1200A then the secoundary level current for different Cts will not be same.
Lets analyse them indivisually.
1) The 800/1 Ct will read it as 1.5A. For that we can simply use Over current relay and trip the breaker.
2) The 400/1 Ct will read it as 3A . here we can use IDMT relay.
As per its function it will sends trip command to the breaker as soon as possible...because here the time of trip is inversely proportional to the amount of fault current
3) But however in case of 200/1 CT, it will read it as 6A. If it is a metering CT then it should be protected 1st. because it has less saturation point as compared to protection or back up CT. So here we will use instantaneous relay so that it will trip suddenly when the fault current goes above some pre defined value.
| Is This Answer Correct ? | 0 Yes | 3 No |
What is the minimum load that you can keep in a 3 Phase 40 KVA Diesel Generator? Is it neccessary to load all the 3 phases? Can a phase be left without load?
What do you mean by cold shinkable cable joint.How it is done.
what is looping circuit in electrical lighting circuits?
How can we estimate Gen rotor current?
i have one ground earth for my shop but now he showing 11v how ever my machine engineer said that he require less than 3v how can we reduce it, i have put 8 bucket salty water in it
please tell me, how i clear the objective test? when i studied form the one book after i solved the objective ,that time i solved that qes. but if i tried solve objective form the other book then i could not solved these que.
induction 3 phase motor terminal connection
What is the use of arc chute in ACB?
differtiate between energy consevation and energy efficiency..
What is the purpose of reactor in over head transmission line.Can you any explain it.
2 Answers Dr Reddys, L&T, Reddy Labs,
How can we calculate D.C.Load current in terms of A.C. load current?
how to cal calculate capacitance in DC Circuit
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)