In a panel 2500A ACB is the incoming breaker then what is
the size of the bus bar?
Answer / rsundareee
The Busbar shall be 3P+N+E =2R x 150mm x 10mm each R,Y,B,N
and Earth Busbar shall be 1R x 150mm x 10 mm.and 85kA for
breaking capacity of the Bus bar.
| Is This Answer Correct ? | 5 Yes | 1 No |
Difference between Earthing Truck & Earthing trolly for HT panel
In Power transformer oil temperature or winding temperature will be high
What is meant by term Back to back in HVDC transmission?
How can we estimate Gen rotor current?
What happened ,If 3 phase clearance not maintained in 33KV Line,11KV LIne etc?
For maintenance Department What type documention requir for ISo & TS audit
1 Answers Megatron Solutions, Sams,
What is partial discharge in power cable?
What is the fullform of IPS in substaion using Aluminium Tubes
why the active power flow of some line is increased when the active power of out is cut ?
how to calculate the neautral earthing conductor size for a 500kva dg set.
i am confused about generator. i have generator of 380 KVA that is 304 KW by that formula KW=KVA*0.8... then by this formula I=KW/V*1.732*0.8 the amperes are 528.673. so that is the load which i put on one phase of generator or this is total 3 phase load on Generator.......
Difference between a pilot wire and a normal conductor?
0 Answers United Arab Aluminum Company,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)