Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


what is the diff between earth leakage relay and earth
fault relay?

Answers were Sorted based on User's Feedback



what is the diff between earth leakage relay and earth fault relay?..

Answer / arnab

sensitivity of earth leakage relay is more than earth fault
relay. earth leakage relay is connected with core balance
current transformer.

Is This Answer Correct ?    37 Yes 5 No

what is the diff between earth leakage relay and earth fault relay?..

Answer / rajdip thakur

Earth fault relay trips when the current through the neutral exceeds a preset value.Simply it acts on the superposition theorem. Whether the vector sum of the phase current and the neutral current are same or not.If not then it operates.
But the earth leakage circuit breaker operates when some current flows from neutral to ground. We know that the voltage difference between neutral and ground is zero.It operates only when there appears some voltage.

Is This Answer Correct ?    14 Yes 6 No

what is the diff between earth leakage relay and earth fault relay?..

Answer / tina john

Eath fault implies a significant contact between phase and ground and it can cause heavy current and can cause damage; earth leakage is a high resistance contact with earth that the phase may have in cables; devices etc.; since the current is small it wont create any problem usually. However, its a sort of indication that there are insulation problems present in the cable/devices.

https://automationforum.in/t/what-is-difference-between-elr-and-efr/173

Is This Answer Correct ?    6 Yes 0 No

what is the diff between earth leakage relay and earth fault relay?..

Answer / govarthinam

Hi radhika

Where u find the Earth leakage relay and Earth fault
relay?pl specify the application.

Regards
Gova

Is This Answer Correct ?    6 Yes 3 No

what is the diff between earth leakage relay and earth fault relay?..

Answer / gunasekaran

earth leakage relay are sensitive earth fault relay. both
are working same principle residual current method.first
one is we r using CBCT second one is ordinary CT.

Is This Answer Correct ?    9 Yes 13 No

what is the diff between earth leakage relay and earth fault relay?..

Answer / mrt

both the relay are same, both relay are operated through
the core balanced circuit breaker. normally the cbct
contains the current(say nuetral current ) is zero. at
balanced condition the neutral current is zero. in case any
fault(insulation,ground fault..) in the line the neutral
current will change from zero. this will operated the relay

Is This Answer Correct ?    4 Yes 13 No

what is the diff between earth leakage relay and earth fault relay?..

Answer / ramniveth

both are same

Is This Answer Correct ?    8 Yes 21 No

Post New Answer

More Electrical Engineering Interview Questions

Can any body tell me about INNER SHUNT COMPOUND MOTOR diagram?

0 Answers  


in a distribution board,if we have a load and we have selected a cable after making all calcs (Deratings and V.D , ect...) the cable we have selected was 10mm.sq. now, shall the internal cable inside the switchboard should be 10 mm.sq Like the external or it can be Less???? if somebody have an specs or information he can help D:

1 Answers  


Under wat condition statcom operates as an inductor for the transmission line?

0 Answers  


why we grounding the neutral of a transformer?

3 Answers   GAS,


What is an iron loss or core loss pi?

0 Answers  


Why is a thicker conductor necessary to carry a current in A.C.as compared to D.C. ?

1 Answers  


does the transmission line model also requier active power in no-load operation?

1 Answers  


How much load can be taken for chiller from 1500 kva transformer

0 Answers  


how i prepare for the written test in mahagenco?

2 Answers   MahaDiscom, MahaGenco, Wipro,


Why electricity in India is in the multiples of 11 like 11kv, 22kv, 33kv

2 Answers   KPIT,


The iron loss in a 100kva transformer is 1 kw and full load copper losses are 2 kw, then what is maximum efficiency occure at a load?

3 Answers   MPSC,


application s to shunt coil

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)