what is the diff between earth leakage relay and earth
fault relay?
Answers were Sorted based on User's Feedback
Answer / arnab
sensitivity of earth leakage relay is more than earth fault
relay. earth leakage relay is connected with core balance
current transformer.
Is This Answer Correct ? | 37 Yes | 5 No |
Answer / rajdip thakur
Earth fault relay trips when the current through the neutral exceeds a preset value.Simply it acts on the superposition theorem. Whether the vector sum of the phase current and the neutral current are same or not.If not then it operates.
But the earth leakage circuit breaker operates when some current flows from neutral to ground. We know that the voltage difference between neutral and ground is zero.It operates only when there appears some voltage.
Is This Answer Correct ? | 14 Yes | 6 No |
Answer / tina john
Eath fault implies a significant contact between phase and ground and it can cause heavy current and can cause damage; earth leakage is a high resistance contact with earth that the phase may have in cables; devices etc.; since the current is small it wont create any problem usually. However, its a sort of indication that there are insulation problems present in the cable/devices.
https://automationforum.in/t/what-is-difference-between-elr-and-efr/173
Is This Answer Correct ? | 6 Yes | 0 No |
Hi radhika
Where u find the Earth leakage relay and Earth fault
relay?pl specify the application.
Regards
Gova
Is This Answer Correct ? | 6 Yes | 3 No |
Answer / gunasekaran
earth leakage relay are sensitive earth fault relay. both
are working same principle residual current method.first
one is we r using CBCT second one is ordinary CT.
Is This Answer Correct ? | 9 Yes | 13 No |
Answer / mrt
both the relay are same, both relay are operated through
the core balanced circuit breaker. normally the cbct
contains the current(say nuetral current ) is zero. at
balanced condition the neutral current is zero. in case any
fault(insulation,ground fault..) in the line the neutral
current will change from zero. this will operated the relay
Is This Answer Correct ? | 4 Yes | 13 No |
A circuit breaker is a
how many BUSBAR is in electrical system?
Active power= VI COS FI But incase of leading power factor ( more than unity), may we use other formula ? because the cos fi (value of cos thita) should not be grater than one.
how to calculate the multiplication factor in HT incomer trivector meters
9 Answers Dalkia, Getco, Gujarat Energy Transmission Corporation Limited GETCO,
What is the function of a neutral reactor.
what is the sludge current
How does and Earth Fault Relay operates in DG set control panel?
1 Answers Cummins, University,
What is the meaning of floating point earthing in battery backed systems ?
why do MCB melt but not tripped in lighting highmast??
Does the total power means fundamental plus Harmonics?
what r Grid stations?what r there role.Explain in detail
CAN 50Hz transformer work at 60 Hz power supply? if yes how it is possible?