Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


what is the diff between earth leakage relay and earth
fault relay?

Answers were Sorted based on User's Feedback



what is the diff between earth leakage relay and earth fault relay?..

Answer / arnab

sensitivity of earth leakage relay is more than earth fault
relay. earth leakage relay is connected with core balance
current transformer.

Is This Answer Correct ?    37 Yes 5 No

what is the diff between earth leakage relay and earth fault relay?..

Answer / rajdip thakur

Earth fault relay trips when the current through the neutral exceeds a preset value.Simply it acts on the superposition theorem. Whether the vector sum of the phase current and the neutral current are same or not.If not then it operates.
But the earth leakage circuit breaker operates when some current flows from neutral to ground. We know that the voltage difference between neutral and ground is zero.It operates only when there appears some voltage.

Is This Answer Correct ?    14 Yes 6 No

what is the diff between earth leakage relay and earth fault relay?..

Answer / tina john

Eath fault implies a significant contact between phase and ground and it can cause heavy current and can cause damage; earth leakage is a high resistance contact with earth that the phase may have in cables; devices etc.; since the current is small it wont create any problem usually. However, its a sort of indication that there are insulation problems present in the cable/devices.

https://automationforum.in/t/what-is-difference-between-elr-and-efr/173

Is This Answer Correct ?    6 Yes 0 No

what is the diff between earth leakage relay and earth fault relay?..

Answer / govarthinam

Hi radhika

Where u find the Earth leakage relay and Earth fault
relay?pl specify the application.

Regards
Gova

Is This Answer Correct ?    6 Yes 3 No

what is the diff between earth leakage relay and earth fault relay?..

Answer / gunasekaran

earth leakage relay are sensitive earth fault relay. both
are working same principle residual current method.first
one is we r using CBCT second one is ordinary CT.

Is This Answer Correct ?    9 Yes 13 No

what is the diff between earth leakage relay and earth fault relay?..

Answer / mrt

both the relay are same, both relay are operated through
the core balanced circuit breaker. normally the cbct
contains the current(say nuetral current ) is zero. at
balanced condition the neutral current is zero. in case any
fault(insulation,ground fault..) in the line the neutral
current will change from zero. this will operated the relay

Is This Answer Correct ?    4 Yes 13 No

what is the diff between earth leakage relay and earth fault relay?..

Answer / ramniveth

both are same

Is This Answer Correct ?    8 Yes 21 No

Post New Answer

More Electrical Engineering Interview Questions

3phase motor 400v (induction) A.C 4kw company design 1400rpm but our requirement 2000rpm possible? attached any instrument. reply fast! contact 03343262442

3 Answers  


what will be happen if earth point is being used for as a neutral point for raw power , and same will be used for ups earthing

0 Answers  


There are two nos of 33Kv/11Kv 5MVA transformers conecting through HT cable from substation having metering at substation itself.One transformer used at a time another remains stand by.Further 11 nos of 11Kv/440V transformers are attached on it and each transformer is having its own Power factor correction panel.Now one 33/11Kv transformer at no load condition/Stand by condition is having power factor in leading side upto 0.21 and while when another tranformer at same situation have power factor in lagging 0.42. Now one thing is clear that transformer one is having 1.5 Km long 33kv cable due to that PF goes in leading side and another is having only 250 mtr length remains him lagging. Now i want to know that how i can maintain the Power factor at no load/ stand by position though both are behaving in seperate manner.

1 Answers  


3 measuring instrument for transformers?

5 Answers  


How to operate a ac chilar plant?

0 Answers  


Difference between 3.5 core and 4 core

2 Answers  


What is the meaning of ST and HT in electrical transmission and what are thier range.

6 Answers  


what is the reason of capacitor failure in alternator which is working with 10 kva dgset

0 Answers  


how LT meggar works

1 Answers   Essar,


what is the function of rccb how it diffrentiate between elcb

1 Answers  


I have an 15A fuse MCB that controls a night storage heater. It needs replacing and is now obsolete. Is a 16A C curve MCB the correct replacement?

2 Answers  


what is the significance of KV & MVA rating of the transformer and how they are related.

8 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)