Why the voltage n frequency of the incoming generator is kept slightly higher than d grid voltage n frequency while synchronization ?
Answers were Sorted based on User's Feedback
Answer / raul
Theoritically it is like dat only dat the frequency n voltage of the incoming machine must match the grid frequency n voltage for proper synch, but practically it is kept slightly higher in order to reduce the impact on speed governor n automatic voltage regulator bcoz as the grid pulls d generator into synchronism, there is sudden load applied on d generator due to which there is a dip in both frequency n voltage of d generator which is 2 b corrected by the speed governor by opening d turbine valve more n more steam enters into turbine which corrects d dip in frequency n on d other hand d AVR corrects d dip in voltage by giving d signal 2 d pilot exciter to give more excitation 2 d rotor field winding of d generator.
I hope d concept is now clear 2 u......
| Is This Answer Correct ? | 9 Yes | 3 No |
In theory the frequency and voltage should match exactly.
In practice the incoming generator voltage and frequency
should be slightly hogher than the grid.
This is to prevent the set from tripping on reverse power
or kva. The incoming generator will pick up some load
straight away so the frequncy and voltage matches the grid.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / raul
Please read some quality books first b4 answering such questions......... but still thnx for some brainstorming
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / b goutham
Actually the condition for synchronization is voltage and frequency of incoming generator should be equal to the grid otherwise there will dead short cicuit...and also large currents flows through the incoming alternator which may damage the winding of the alternator.....so the voltage and frequency should be the same...
| Is This Answer Correct ? | 0 Yes | 6 No |
is high voltage or high current is danger
how we can know the rating of transmission line by no. of insulators disk ??????????
what is the significance of terminal voltage and phase sequence in the operation of paralleling of two generators?
why 3 phase is converted into 2 phase using electronics circuit why not 2 phases are diresctly putted from the 3 phase transformer??
Can Induction motor run at over rated speed? ( 15oo rpm is rated speed for 50HZ. is it possible to ride 3000 RPM with same motor with the help of VVVFD for continues ride of 100HZ)
what is the difference between relay, contactor
4 Answers BRSS, Vishay Intertechnology,
sir pls send the je exam - 2008 and other model question papers..
why we don't use air circuit breaker on H T line in place of vacuum circuit breaker ?
In the formula : Knee point voltage = Burden X alf / class, Please inform what is alf? regards Shashidhar M.R.
what is the principle of switchgear and its function
what is the fullform of mccb
what is transformer
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)