Why the voltage n frequency of the incoming generator is kept slightly higher than d grid voltage n frequency while synchronization ?
Answers were Sorted based on User's Feedback
Answer / raul
Theoritically it is like dat only dat the frequency n voltage of the incoming machine must match the grid frequency n voltage for proper synch, but practically it is kept slightly higher in order to reduce the impact on speed governor n automatic voltage regulator bcoz as the grid pulls d generator into synchronism, there is sudden load applied on d generator due to which there is a dip in both frequency n voltage of d generator which is 2 b corrected by the speed governor by opening d turbine valve more n more steam enters into turbine which corrects d dip in frequency n on d other hand d AVR corrects d dip in voltage by giving d signal 2 d pilot exciter to give more excitation 2 d rotor field winding of d generator.
I hope d concept is now clear 2 u......
| Is This Answer Correct ? | 9 Yes | 3 No |
In theory the frequency and voltage should match exactly.
In practice the incoming generator voltage and frequency
should be slightly hogher than the grid.
This is to prevent the set from tripping on reverse power
or kva. The incoming generator will pick up some load
straight away so the frequncy and voltage matches the grid.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / raul
Please read some quality books first b4 answering such questions......... but still thnx for some brainstorming
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / b goutham
Actually the condition for synchronization is voltage and frequency of incoming generator should be equal to the grid otherwise there will dead short cicuit...and also large currents flows through the incoming alternator which may damage the winding of the alternator.....so the voltage and frequency should be the same...
| Is This Answer Correct ? | 0 Yes | 6 No |
Which lamp will fuse first(1)20(2)40(3)200 three lamps will fuse together
if i get a drop in my 1st year and the i clear my 2nd year and 3rd year all clear and i dont have any back logs so can i be able to sit in campus selection??
how can we calculate that how much capacitor is needed for a system to increase the pf?
What is a Phase shift meter? Where can I get one?
what is difference between single phase and three phase.
How can i calculate knee point voltage of 800/5A Current transformer?please explain me with suitable calculation?
1.what is use of isolation transformer. 2.Differance between KWH,KVAH,KVARH,KVA. 3.Main use of the CT and PT.
the circuit having same properties in either direction is known as.......
If the Brush of DC motor is shifted by 90 deg, then what happens to voltage and torque? Both voltage and torque are zero. how to justify the answer?
how starting current in motor is reduced in case of motor in star connection.
how much capacity(rating) of generator required to operate a load of 100kv.
what is the operation of regulator in fan?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)