The midpoint of rectifier transformer secondary is
earthed.The potential of ground is taken as +/- 0.The
voltage measured between any terminal wrt ground will be +/-
half the full voltage.This method is helpful to trace a
single polarity and for earth fault locator.
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / sarvesh kotiyal
Because your Ground is not connected with V-(V- which is taken as reference point). when you check Voltage respect to ground that time you should also check the resistance between V+ to E & V -E which is equal(the Value which is higher than 10 mega ohm ).
Simple apply voltage Divider & you will get half Voltage
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / koti
The value shown is a capacitive value i.e it is due to capcitance effect wyou are getting some value. If you put a lamp it will not glow.
| Is This Answer Correct ? | 2 Yes | 2 No |
The above answer is correct.If you use an earth fault
indicator ,you are able to measure voltages. And if you run
both leads along the ground or a metal surface ,you can
measure voltages with a digital voltmeter ,as the
capacitances between the leads and the surface/ground, bring
the surface/ground to +or- zero potential.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sarvesh kotiyal
the resistance between the supply and ground is very high(1-5gohm). so Ideally it should not show any voltage but Internal Input resistance of multimeter approx 10 Mohm for Voltage measurement which is almost a short circuit in comparison to earth .so when you check voltage with respect to earth
V + to E = 24 * 10/10+10 = 12 V.
| Is This Answer Correct ? | 2 Yes | 2 No |
What is the difference between newtral earthing and body earthing?
3 Answers JK Lakshmi Cement, NPCIL,
What is complex power?
what about the power of wattmeter at starting and loding?
what is use of starter motor in DG ?
Determine the MVA rating of the power transformer given that 110/66 kV,1000 Amps. Folks how can i calculate the MVA rating with this Data??Plz Help........
What is the difference between generator and turbo generator - related to power gereration
How power factor of a transformer is calculated
in control panel, how can i measuring the distance between one bus bar to another bus bar. then now only for bus bar. in mpcb and contactor also. that means one mpcb to another mpcb how much distance? how can i calculate that.
following are the questions asked in interviews: 1) Considering the short circuit fault, which switchgear is preferable, SFU OR MCCB? Which operates faster? whicg one is popular in Indian Market and why? 2)Define SCPD. What is type2 coodination? 3)Why the contactor rating is higher for the fuseless selection than for fuse selection? whether the ratinf of SFU or MCCB remains the same in both the cases? 4)If the HP rating is known then can you calculate the ratings of L.V Switchgear(SFU/MCCB, contactor, OLR) without using the selection chart?
WHAT IS DIFFRENCE BETWEEN 3 PHASHE AND 1 PHASHE
quantizer means?
In view of Electrical Engg. What is the use of SCR(Silicon control rectifier)
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)