Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


why dont we connect the two 12 V DC batteries in parallel,
for an inverter (UPS)?

is there any harm ?

Answers were Sorted based on User's Feedback



why dont we connect the two 12 V DC batteries in parallel, for an inverter (UPS)? is there any ..

Answer / aamod tripathi

NO HARM BUT THE SIZING WILL BE DIFFERENT IN THAT CASE

Is This Answer Correct ?    6 Yes 0 No

why dont we connect the two 12 V DC batteries in parallel, for an inverter (UPS)? is there any ..

Answer / ashwin

For what purpose you are going to connect the two batteries? To increase the voltage you have to connect the batteries in series not in parallel. If you want to increase the current then connect the batteries in parallel.

For further knowledge on the series and parallel connection of the batteries go to the link below:

http://batteryuniversity.com/partone-24.htm

Is This Answer Correct ?    6 Yes 0 No

why dont we connect the two 12 V DC batteries in parallel, for an inverter (UPS)? is there any ..

Answer / hari

No harm in connecting batteries in parallel of same capacity, it will increase the Ampere hour capacity,

Is This Answer Correct ?    4 Yes 0 No

why dont we connect the two 12 V DC batteries in parallel, for an inverter (UPS)? is there any ..

Answer / lokeshraj

If the batteries are identical there is no problem in
connecting parallel, but if the internal resistances are
different then there will be a circulatery current in
batteries as in transformers... this may heatup the
batteries.

Is This Answer Correct ?    2 Yes 0 No

why dont we connect the two 12 V DC batteries in parallel, for an inverter (UPS)? is there any ..

Answer / dinesh desh

what do you mean by sizing will be different

u want to say that size of the UPS' unit will be bigger or
what ?

would you kindly explain this to me ?

Is This Answer Correct ?    0 Yes 0 No

why dont we connect the two 12 V DC batteries in parallel, for an inverter (UPS)? is there any ..

Answer / international ups imports and

there will be no harm for ur ups if u connect so.the only
thing is going to happen is it will increase ur backup time.
but u have to take care of ur circuit inbuilt initially as
there may be a chance of over currents when power
fluctuations occur like low voltage for long time,etc

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

what is the definition of Nominal current or voltage

1 Answers  


what is the main parts of transformer? how it is functioning? pls giv the ans briefly.

0 Answers  


why transformer is rated in KVA ?

5 Answers  


I have 30KW Motor Starter Panel, System voltage is 480V, So i have to convert voltage 480 to 220V to give the contactor coil. How i can select control transformer, Which rating transformer i can use this panel, what is the procedure, please tell me.

2 Answers  


In supply RYB are mentioned. But in transformers, why they are mentioning XYZ?

3 Answers  


If a 3 phase transformer is a 500 kva using the formulae 500kva= 500000/433 x 1.732 = 666.71amps does this mean that each phase on the secondary side is 666.71

3 Answers   Saffron,


What is dynamo?How it works and what is the function of dynamo in a DG.

3 Answers   Amrapali,


Reason of secondary of ct always short

5 Answers   ANITS, EID Parry,


3 phase =440v single phase = 230v 2 phase =?

8 Answers   Accenture,


what is armature reaction?explain in simple words?and what is its infleunce on dc motor

16 Answers  


how many testing use in power transformer?tell equipment names?

2 Answers   ABB, Electrical,


WHAT DO U MEAN BY THERMAL OVER LOAD RELAY& WHERE THEY ARE BUSED

4 Answers   L&T,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)