why battery dc voltage become Half when we check with
respect to ground for example 120volts + and - terminals
and when we check + terminal with Earth thats 60volts why
60volts we can not ground the battery.
Answer Posted / sarvesh kotiyal
the resistance between the supply and ground is very high(1-5gohm). so Ideally it should not show any voltage but Internal Input resistance of multimeter approx 10 Mohm for Voltage measurement which is almost a short circuit in comparison to earth .so when you check voltage with respect to earth
V + to E = 24 * 10/10+10 = 12 V.
| Is This Answer Correct ? | 2 Yes | 2 No |
Post New Answer View All Answers
How does PLC work for sychronising of Two or more DG sets?
What is knee point voltage of transformer?
how can we change the polarity of Alternating current rapidly? how frequency of ac can be controlled and changed easily?
What is electrical diversity factor in electrical installations?
-How do you select cable size for a given load at a given distance from source of supply. How do you find voltage drop.
What is the unit audit? if our Max demand is something and we found much more unit then how to improve our max demand?
aternator every parts and its working
gas turbine genrator reactances
What are the applications of the electric motors?
UG cable sizes were specified in sqmm. But practically its not coming to mesure. What's the reason for that? And how they specify the size of the cable?
Why does the rotor rotate?
how to determine Sq.mm size of finolex power cables.
WHY IL=IPH IN STAR AND WHY IPH=IL/1.732 IN DELTA? WHAT IS REASON BEHIND IT?
TRANSFORMERS WITH DC SUPPLY
WHY RATING OF VCB NOT LESS THAN 630A