why battery dc voltage become Half when we check with
respect to ground for example 120volts + and - terminals
and when we check + terminal with Earth thats 60volts why
60volts we can not ground the battery.
Answer Posted / sarvesh kotiyal
Because your Ground is not connected with V-(V- which is taken as reference point). when you check Voltage respect to ground that time you should also check the resistance between V+ to E & V -E which is equal(the Value which is higher than 10 mega ohm ).
Simple apply voltage Divider & you will get half Voltage
| Is This Answer Correct ? | 1 Yes | 0 No |
Post New Answer View All Answers
On what principle electric motor works?
what is errection pcbs?
where the lexical paramater will use in fron end?
what happens to the water pump if ground water level is slowly decreasing?our water pump is varying from no-load full-load due to this problem
WE know that for Inductor X=2pifL,In DC f=0,then X=0 so,V=IX=0;But In the DC excitation of rotor of AC generator,DC motor field coil which coils are inductor so why does not applying DC voltage short the rotor coil of AC generator and field coil of motor?If it would then DC source might be damaged but it is not happened. Why does the strand conductor of Electrical power transmission line make twist?
what is the stear deltaprinceple?
define the non synchoronism of synchoronous machine in general g or m??
How to calculate the value of earth capacitance in a transmission line.
What are the types of feedback oscillators?
What are the factor to be consider for CT selection in 132kV substation?
What is power relay?
brief notes on ammeters
why tertiary winding is used in transformer with diagram?
What do you mean by distribution transformers?
star delta starter contorl circuit... drawing..