why there is no grow of grass under the high voltage
transmission line?
Answers were Sorted based on User's Feedback
Answer / vikramsimha reddy
if grass is grown,moisture deposits on the surface of ground
and grass in the areas of moist weather or during winters
which posses harm if any short circuit occurs..
stones or gravel is used
Gravel/Stones in the substation is provided to reduce the
step potential and touch potential when operators work on
switch yard.
Step potential : It is the potential developed between the
two feet on the ground of a man or animal when short circuit
occurs. This results in flow of current in the body leads to
electrical shock
Touch potential: It is the potential that is developed
between the ground and the body of the equipment when a
person touches the body during fault condition. When
operating personnel touch an electrical equipment during
short circuit condition, fault current flows through the
human body. This is defined as touch potential.
Stones eliminate the growth of small weeds and plants inside
the switch yard
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / satis garnayak
dear sir, but my question is why no grow of grass under hv transmission line not in grid station..so plz kindly tell
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / mohammad al fahel
because of the magnetic field since transmission line is high voltage it reaches up to 400 KV so it has a high magnetic field which is harmfull for all creatures for humans and plants , but if you want to plant grass i think its fine since the effective of it is not that big
| Is This Answer Correct ? | 0 Yes | 5 No |
I am interested to know what does 15 KVA DG set actually means? If I dont know the DG rating, is it possible to identify KW by simply knowing the diesel consumption?
Give atleast 20 alternating current apparatus and devices.
What would be the steps and parameters in case if a fault occurs in transmission line at a distance far from the generating station?
What is the current carrying capacity of 0SWG,3SWG,10 & 12 SWG solid bare overhead copper conductors?
In a 11KV 3phase system do you need to earth both sides of the cable?
DERIVE AN EXPREION FOR MAXIMUM POER TRANSMISSION, WHAT ARE ITS APPLICATIONS.
How we can determine short circuiting current any plant and for example a plant which power generation is 415 volts and plant load is 500 kw.
How can we design MEP services for Commercial Building in area about 22 Acres of land?
what is IDMT relay.
what are the Alarm, Trip & Safety equipment (Issues) present in Power Transformers pls Mail it to ashokbabunhce@gmail.com
Why space heater is required for each verical bus bar chamber? if one space heater is adequate or not for anti condensation?
if there is nutral in phase why we use earthing wire and grounding? even at fault condition the fault current flows to neutral (it is a lower path)
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)