We have .ht motor which is 60Hz.we run on 50Hz.so that it's speed reduce
but we had one prob.that motor winding temp increase up to 135 deg.we
want reduce this temp.what to do?we arrange ext.cooling fan but not much
effect.we want reduce this temp. Inhouse without affecting much.cost. also
don't want reWINDING OF MOTOR?
Answers were Sorted based on User's Feedback
You may have to reduce the load more till you get the
desired temp rise
| Is This Answer Correct ? | 1 Yes | 0 No |
As you have reduced the speed ,the cooling effect of the
shaft mounted cooling fan is also reduced .Either you have
to reduce the load by about 10% or replace cooling fan .
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / r c thakur
You have to increase the surface area of the motor,the
radiator fins can be introduced,
| Is This Answer Correct ? | 0 Yes | 0 No |
Why in medium voltage system(3.3kv to 33kv, neutral is earthed with either resistance, reactance or neutral grounding resistance?
How do you select a cable size(Cu&Al) for a particular load
10 Answers Adhunik, BPCL Bharat Petroleum, Hiecon, TATA,
Formula to calculate amps rating when we are having only the width & thickness of the coppper ?
how to select the automotive wire size by mathematical calculation. for xenon headlamp with ballast. the ballast given data voltage 10-17v,current permenant 6amp, run up phase is 15amp, peak at swicth on max 400micro sec is 40amp.the sum of cable resistance is 150mohm.please provide referenc document if any for relating the peak at switch on current,time & wire wire size
Why current flows in nutral? As per theory there should be no current in 3 ph explain.
In a d.c current, the power is the product of voltage and current. This relationship does not always apply to effective(r.m.s) values in an a.c circuit. Explain the reason for this.
can we use the step down transformer to step up transformer
Is there any problem ,if R-Y-B voltage is constant , but the air compressor taking one phase high current.what is possible causes.the said compressor is very new.(55kw).
how tto ingress mw in turbine explain.procedure ?
is a normal conductor can be used a core in windings if not what is the winding core speciality.
Which power will flow first if we switch on a motor? Active or Reactive? How?
Is there any specialised book to refer about fault level calculation both in MV and LV side??
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)