We have .ht motor which is 60Hz.we run on 50Hz.so that it's speed reduce
but we had one prob.that motor winding temp increase up to 135 deg.we
want reduce this temp.what to do?we arrange ext.cooling fan but not much
effect.we want reduce this temp. Inhouse without affecting much.cost. also
don't want reWINDING OF MOTOR?
Answers were Sorted based on User's Feedback
You may have to reduce the load more till you get the
desired temp rise
Is This Answer Correct ? | 1 Yes | 0 No |
As you have reduced the speed ,the cooling effect of the
shaft mounted cooling fan is also reduced .Either you have
to reduce the load by about 10% or replace cooling fan .
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / r c thakur
You have to increase the surface area of the motor,the
radiator fins can be introduced,
Is This Answer Correct ? | 0 Yes | 0 No |
what is the minimum (Common factor) insulatin resistance of the following a, 4mm sq wire b, cable from 50 mm sq to 800mm sq
why alternator is used instead of dc generator and induction generator
how to find out three phase motr kw with out name plate..
If 22 KV HT line, Current transformer is 25/5 then how to calculate multiplying factor.
why voltage drop will occurs in 3 phase line?
What is d diff. btw MCB & MCCB???
How is operate breaker failure scheme in substation
In liquid rotor starter how PH valve should be maintained.
A 400KVA transformer has 400 Hz frequency. If the frequency is changed to 50 Hz, then what will be the new KVA rating?
How do i perform grounding of star point of Genset (400V) for making connection with step up transformer of DELTA-DELTA (400V to 20KV) ? while Genset itself has its own neutral and grounding bus bar inside genset breaker box whereas we have another neutral and grounding busbar in synchronizing panel next to genset at maximum distance of 6meter, would someone pls advice if we can only perform neutral grounding in synchronizing panel or should we ground neutral on both places inside genset breaker box and synchronizing panel.
What do you mean by reach and reach the point of the relay?
How to measure the Harmonic Distortion of UPS ie THD?