T.x range -0.1 to 0.2 milibar,so how much mili ampear at 0.1 milibar?
Answers were Sorted based on User's Feedback
TX range is -0.1mbar to 0.2mbar
span= maximum-minimum
= 0.2-(-0.1)
= 0.3
mA = given value- zero value/ span x 16+4
= 0.1-(-0.1)/0.3 x 16+4
= 0.2/0.3 x 16+4
= 14.66 mA
| Is This Answer Correct ? | 8 Yes | 2 No |
Answer / sampath
LRV = -0.1 mbar
URV = 0.2 mbar
SPAN= 0.3 mbar
( 0.2/0.3 )* 16 + 4 = 14.67 mA @ 0.1 mbar
| Is This Answer Correct ? | 11 Yes | 9 No |
Answer / dibyendu das
tx range= -0.1 to 0.2millibar
span =0.3
-0.1 = 4 mmA
-0.075 = 8 mmA
+0.05 = 12 mmA
+0.075 = 16 mmA
+0.2 = 20 mmA
this is the ratio to calculate 0.1 milibar = how much amps.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / sarath kumar
tx range= -0.1 to 0.2millibar
span =0.3
hence, mA at 0.1 miilli bar = 9.28 mA
| Is This Answer Correct ? | 4 Yes | 13 No |
why we us isolation barrier in hazardous area how it works to protect the area and please clarify its current flow.
In turbine, what does term CDP, NI, NH, HSSOC, means
can i use capillary type dp transmitter converted to capillary type pressure transmitter. if i removed one side capillary tube its work correctly?
If a differential pressure transmitter is calibrated for 0~2500 mmH2o and transmits a 4~20mA dc signal. The transmitter is placed across an orifice plate which is sized to create 2500 mmH2o differential at 5000m3/Hr a) what is the flow rate when the transmitter signal is 13.0mA DC? b) what is the signal output of the transmitter when flow rate is 2500 m3/Hr ?
open tank and close tank leavel transmiter about range and calibration
How to calibrate the pressure Transmitters
Define all the process Variable and state their unit of measurement. ?
How can a d.p. Transmitter be calibrated?
Why the ammonia and Nitric Acid level indicators is with millimeter ? and What is the conversion form millimeters that level indicator indicate to weight ?
WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?
What is meant by GAP VOLTAGE, in vibration measurement. Normally how much GAP VOLTAGE is set and state the reason.
HELLO FRIENDS PLZ EXPLAINE ME WHAT IS ORIFICE?AND HOW WE ARE USING IT IN INSTRUMENTATION
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)