how to test a motor from megger
Answers were Sorted based on User's Feedback
Answer / r.kumar
for megger test in motor.......we apply 500v DC supply at terminals and check:
1.phase 2 phase(ohms)
2.phase 2 body (>100MEGA OHMS OR GIGA OHMS)
3.phase 2 neutral(>1 GIGA OHMS)
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / bameshwar
To identify the motor winding is correct or not. Body to coil and coil to coil for identify the motors coils shorted or not. It's values are body to coil-infinity or more than 5megaohms,coil to coil - 0megaohms,and coil to othercoil-we are seeing the insulation between coils
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / bameshwar
To check the winding s of motor is correct or not (motor shorted or ready to run) it's values are body to coil-infinity, and the coil to coil - 0megaohms, & coil to other coil we are seeing insulation between coil to other coil which is according to motor.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / avvsnmoorthy
motor winding meggar value from bofy t0 phase more tham 5
mega ohm &winding to winding 0 with using 500 volts megger
| Is This Answer Correct ? | 2 Yes | 4 No |
single phase power supply give to separate one steel coup with water, what reaction create
what is the difference between series and shunt compensation using facts in a transmission line
8 Answers College School Exams Tests, Genco,
if step down transformer step down the voltage,will current will also be proportional step up. If yes then how transformer handle such a large current?
How to select the proper VSD to operate high inertial load
what is the difference between AC choke (inductor) and DC choke (inductor), working and design point of view?
1 ph induction motor winding priniple and connection diagram?Similarly for 3 ph induction motor?Full description
what are the applications of PLC?
What is the difference between earth fault protection of motor feeder with CBCT and Without CBCT ?
0 Answers Enmas, Michelin, Reliance,
What is burden of a current transformer. What is function of core in Transformer
1 Answers Jindal Steel and Power, NCC,
if the number of poles generated in stator and rotor side of an induction motor are different then what will happen and why?
single phase can run in PVC conduit. Three phase can also run in one PVC conduit. But two phase cannot run in one PVC conduit. WHY? reply plz....awaiting your answer.
Is there any problem ,if R-Y-B voltage is constant , but the air compressor taking one phase high current.what is possible causes.the said compressor is very new.(55kw).
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)