Answer / rashid al-hadifi
Series capacitive (series compensation).
To reduce the total reactive power(MVAR)loss.
Shunt capacitive (Shunt compensation).
To improve system power factor.
| Is This Answer Correct ? | 50 Yes | 10 No |
Answer / chatinder
shunt compensation is to improve voltage profile.....series compensation is for system stability.
| Is This Answer Correct ? | 23 Yes | 8 No |
Answer / kailas vanvas singade
Series compensation reduces risk factor hence it is used to hit the current thermal limit.
| Is This Answer Correct ? | 10 Yes | 1 No |
Answer / monali bhise
Shunt compensation improves power factor of load whereas series compensation has very little effect on load power factor. For a long transmission line where total reactance is large, series capacitors are more effective for improvement of stability.
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / mirza
In series compensation voltage is injected into the transmission line while in shunt current is injected....
| Is This Answer Correct ? | 6 Yes | 6 No |
Answer / anurag_jammed@yahoo.co.in
by compensation we mean reducing losses,if the load at user
end is inductive in nature we use shunt compensation
(capacitive in nature) while if the load at user end is
capacitive we use series compensation(inductive in nature)
| Is This Answer Correct ? | 10 Yes | 25 No |
Answer / saida
compensation is required to put the constant voltage at
receiving end.
the both series and shunt commentators are same but in the
case of series compensator the losses will be more.
| Is This Answer Correct ? | 5 Yes | 21 No |
i have one ground earth for my shop but now he showing 11v how ever my machine engineer said that he require less than 3v how can we reduce it, i have put 8 bucket salty water in it
how to fit 3 HP crompton gear motor with conveyor with the use of staring delta starter or ordinary starter?
i have a 4 Mva transformer 34.5 kv / 480-277 v and i used 2 parallel 3200 amp bus duct for the secondary feeder using 3 ply of bus bar ( 3/8" x 5" ) as a common where the flexible link terminated and 6300 amps breaker for the main, the lower bus duct reaches 70 degrees and the upper bus duct reaches 55 degrees when i used thermal scanner. why the temperature is not balance when the load reaches 3600 amps.
what is the resistance value of our human body?
In 11KV Double pole structure for each phase we are using Disc one Insulator. Why we are not using 2 r above insulators instead of one insulator?
What is a liquid resistance starter?where it is used??
750kva 11/415kv transformer having percentage impedence is5.64%. 11KV HV whose current 39.37A and 415V LV whose current 1043.43A.resistance is 2.5ohm. find no load loss and full load loss?
why we r using alternator instead of d.c generator and induction generator
we have 400kv/6.6kv transformer ,it has total 9 taps on HV side with normal tap on tap no 5.when we took the ratio test we observed that ratio was decreasing from tap 1 to tap 5 and was found increasing from tap 5 to tap 9.What is the reason?if anyone have related document then please send me on the email id ankushbahale@gmail.com......plz plz
What is the latest generation of circuit breakers called?
how and why are capacitors are used to improve powerfactor?
if single phase is 230 v three phase is 440 v then what about two phase?and why is it so?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)