there is a power transformer 66/11kV in delta-delta
connection has 5 feeder coming out from the secondary side.
One of the feeder in it normally loaded (loaded than other
feeder)and this feeder usually trips with double OCR causing
the bank transformer to trip. Now if the load of this feeder
is put on other transformer then that no problems occurs on
that transformer or the load. However normally all the
test(IR, PI, short ckt, open ckt,grounding test and other )
has been conducted for this but evertything transformer.....
I am not geting what is the actual problem...
Answers were Sorted based on User's Feedback
Answer / parin patel
This thing happened dew to %Z of transformer.lesser the %Z current supplied by transformer will be more.
example:- there are two transformer
transformer 1: 66/11 kv,%Z= 5% ,15 kVA
transformer 2: 66/11 kv,%Z= 7%, 15kVA
If load is constant(same), current supplied by transformer 1 at 11 kv is more than current supplied by transformer 2 at 11 kv.
In your case ,you have to check the value of feeder current when it's supplied by two different transformer.in both case it might be different.
| Is This Answer Correct ? | 0 Yes | 0 No |
More data is required for analysis.If the transformers are
of same capacity and relays are identical ,interchange the
relays of transformer banks and watch.
| Is This Answer Correct ? | 0 Yes | 0 No |
if there are six generators (3 gas CATT, one Jenbacher o1 MW each, and two nos Diesel 01 no 01 mw other 0.65mw EDGs ( say), 3 CAtt gas set have identical pole pitch,01mw EDG and Jenbacher gas Set have different pole pitch, how their power connection can be done to connect a common bus bar during installation. in short, how different pole pitched generators power connection can be done to connect a common busbar system through generators incomer ACBs.
what is current
53 Answers Bio Enterprises, CLG, TCS,
Hp to Kw and Kw to I(amps) conversion......
how can I improve the current at same voltage? if yes is there any circuits?
Differentiate between real and apparent power?
why use only sf6 circuit breker in 400 kv sub station
what's the difference between ATS and AMF...??pls answer me in detail with its working principle and construction also..
Why cpaciter opposes sudden changes in voltage?and how?
what are the safety measures of induction motor?
why there is a phase shift lies between primary and secondary voltages of a transformer?
is all the servo motors having brake?please specify which servo motors having brake for stop on position and which are not.
DRAW THE DIFFERENCE BETWEEN GROUND AND NEUTRAL IN BOTH SINGLE PHASE AND THREE PHASE?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)