We have 2 no. 4MW DG set. and GEB supply.
But, we running, only 1 DG set. when we done APFC/Power
factor setting : 0.90, then winding temp. Low. but when
setting done : 0.83, then Winding temp. increase.
WHY Why ? ? ?, plz give me answer.
Answers were Sorted based on User's Feedback
Answer / suthan prabhu
The reacive power taken by the load will be same but the
current supplied by the source will increase bcoz the p.f
is decreased from 0.9 to 0.83.hence the winding temperature
increased.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / gurucharan singh
this is clear that at lower pf settings, its the DG which
compensate for the KVAR. which results in the high winding
temperature. For this check the plant loads connected. And
KVAR supplied by EB & DG. Also during parallel with grid DG
generally act as KVAR compensator along with KW supplied.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / rajnikant dodiya
Simple,
power factor increse, current decrese ane hence losses
(I^2R) reduces. But if Power factor reduces, losses
increases with square of current which makes dg to be hot
compared to increase pf.
| Is This Answer Correct ? | 0 Yes | 0 No |
if we increase the frequency given to a transformer then wat will happen to the transformer size, whether it will increase?
what is the difference between upper impedance and lower impedance distance relay?
3 Answers Havells, Power Grid,
What will be advantage if we put some load in neutral of grounded star transformer & loadshortcircuit current,rated current of cable & MCB with example?
Can any answer me ,What will be the range of C.T coil for L&T energy meter EM301 used for 180 kva DG set
Why transformer rating is represent in KVA?
7 Answers Bhel, Sonalika, Usha Martin, Wipro,
Dear sir, I completed DECE In the year 1995.Now i am working in a private company from last 10 years as an Electrical supervisor.The company having a 1000 KVA transformer.Now i try to apply "C" Licence. I am eligible or not.If not eligible,pls give solution.
when we connect the capacitor bank in series
what are the things that can cause a three phase motor to crawl?
Trafo ratio is 11kV/6.6kv,Vector group is YND11. What will be the effect if secondary is used for earthed system.
why not starting switch first connect in direct on line starter?????
why normally Generator rating are between 11Kv to 22Kv?
Which motor has high Staring current A. Series DC motor, B.Induction motor c.Synchronous motor D.DC Shunt Motor
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)