two or more transformer are working in parallal,one is out
of order,what are you doing?
Answers were Sorted based on User's Feedback
Answer / pramod
Initially reduce the load as soon as possible because it is
running in parallel means both will share the load, if
anyone out of order means the complete load will comes into
one tfr then may it will cause severe major problems.
Is This Answer Correct ? | 25 Yes | 1 No |
Answer / souvik dutta
From an Assistant Engineer's point of view at first I have to inform the Load Dispatch Centre about that transformer which has gone out of order. Then if I have spare transformer I will fix it by putting power to the transfer bus. Otherwise, the remaining transformers will be given to share possible maximum load according to their capacities by adjusting their tap changers.
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / technic man
I think if you have two transformers only and shared a load , then there's nothing to do except rejecting the load immediately because the fault will happen in less than a second
but the main advantage of parallel transformers is when one of them is out of service the others will keep working
so it must be auxiliary transformers in parallel to do that purpose
Is This Answer Correct ? | 5 Yes | 3 No |
Answer / shahbaz shaikh
first of all i will reduce the load and then see wich
transformer is in working and how much load it will carry
and that much load i will apply on it and remain it in
working conditions.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / pramit dutta
The transformers are connected parallel for sharing the load.
if one is out of order then we must reduce the load. then we connect another transformer in parallel instead of it, that can carry the remaining load.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / pramit dutta
If anyone of the transformers run in parallel is out of order
then other transformers in the system will share the load without interruption of power supply. But if this load make the overload for those transformers then according to pramod
immediately we have to reduce the load.Otherwise it will cause
some major problem.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / vinod kumar
whenever one of the transformer operating in parallel gets repair,that particular transformer is replaced by stand by transformer in substation,so that it will not result in damage of the existing transformer due to overloading.
Is This Answer Correct ? | 1 Yes | 0 No |
what is the benefit of floating our DC source? if i have two floating DC source of which 1 has a ref voltage of -21VDC and the other of -18VDC. can it be connected in parallel to share a common ref voltage? if not, how do i make both sources to be of common ref voltage? tks
what is class of SPD and dittels of all class ?
what is the formula for calculating motor rating? Example: If we want to rotate a 1000 kg waight disc up to 100 RPM, which size motor will require?
What is the problem if we connect a weak capacitor to the system? is that profitable or Loss?
no of rotrs poles in salient pole synchronous machine
What is slip in induction motor?
Block diagram of Power line communication?
11 kg trivevter meter has rating of -/5amps. And pt ratio11000/110v and is connected with 11kv ct/pt unit of cr ratio 75/5amps. And pt ratio of 11000/110v while checking accuracy of meter with HT Accuchek meter what value of PT ratio and CT ratio to be filled in Accuchek meter
how to syncronize two dg sets
What is the purpose of Rotor earth fault relay and How to test the Rotor earth fault relay in generators and What is the procedure?.
Can anyone tell me some hints about what type of questions are asked by the interviewer by an Electronics engineer when company is installing an IPP and wants a team of engineers?
why we ht line cable size small rather than lt cable.